Gurgling Sink After Remodel

Users who are viewing this thread

JasonG

New Member
Messages
14
Reaction score
0
Points
0
I have a gurgling sink after a remodel project.

The old setup was a large cement sink in the basement where the washing machine emptied into. This sink had no vent pipe or visable trap, but it worked fine. The drain pipe went right into the cement slab. I assume after this point the drain pipe connects to the main waste pipe which connects to the city sewer.

We replaced this sink and I added a trap and an AAV. We also remodeled the kitchen directly above it and moved the kitchen sink which now drains into the same drain pipe. I added an AAV to this sink as well.

Now, when the washing machine empties into the basement sink, the kitchen sink gurgles a bit.
 

Attachments

  • gurgle.jpg
    gurgle.jpg
    33.2 KB · Views: 910

Master Plumber 101

In the Trades
Messages
268
Reaction score
2
Points
0
Location
Wisconsin
Your Air admittance valve is not installed correctly. It should be either off the horizontal portion of drain before it goes to the 90, or vertical end of a tee min. 4" above trap. That's if it is installed as you have drawn up.

Also check to see if the aav you installed is code approved. My state only allow's Studor vent's to be installed and that will not be for long because of problem's the device is currently having.
 
Last edited:

JasonG

New Member
Messages
14
Reaction score
0
Points
0
Sorry about the bad drawing... AAV is actually installed like in this picture. It is well above the 4" minimum and is probably close to 18" above the trap on both sinks. They are both Studor vents, and Studor vents are approved for use in my area.

Yeah, I probably should have vented it differently than using AAV's and I still might do that to correct the problem.

But... I want to understand why this is happening first. Do you think there is something below the concrete preventing the air from going down and out the main vent?
 

Attachments

  • AAV Setup.jpg
    AAV Setup.jpg
    4.6 KB · Views: 618

Ian Gills

Senior Robin Hood Guy
Messages
2,743
Reaction score
3
Points
0
Location
USA
I had a similar problem when I replaced my concrete sink that WAS properly vented. It turns out that the pipe the utility sink drains into was a little gunky.

After cleaning the pipe out (I used lots of liquid plumber :eek:) the utility sink empties quicker and the gurgling has gone too.
 
Last edited:

Grimace

New Member
Messages
16
Reaction score
0
Points
1
Location
Slater, Iowa
The old setup was a large cement sink in the basement where the washing machine emptied into. This sink had no vent pipe or visable trap, but it worked fine. The drain pipe went right into the cement slab. I assume after this point the drain pipe connects to the main waste pipe which connects to the city sewer.

If it didnt have a trap then wouldnt this sink have vented sewer gas into the basement?
 

JasonG

New Member
Messages
14
Reaction score
0
Points
0
If it didnt have a trap then wouldnt this sink have vented sewer gas into the basement?

You would think so, but that didn't ever seem to be a problem. As I was working on the drain pipes throughout the house, I had several of them wide open, some for extended periods of time, and never smelled any sewer gas ever.
 

Gary Swart

In the Trades
Messages
8,101
Reaction score
84
Points
48
Location
Yakima, WA
I have had a similar experience. I attributed it to the fact the the city sewer main is at least 60 feet away. I don't know if that is a valid conclusion, but for whatever reason, I had no sewer gas that I could detect. I did keep a rag in the pipe anyway.
 

MACPLUMB

In the Trades
Messages
1,080
Reaction score
83
Points
48
Location
HOUSTON, TEXAS
Sink After Remodel

You Have A Partial Blockage And Need To Snake Drain To Clear
And The Noise Will Stop
 

Cwhyu2

Consultant
Messages
1,615
Reaction score
22
Points
38
Location
Cincinnati OH
A lot of old laundry trays with no visable trap drained into 3" traps under
the floor and considered floor drains either direct or indrectley connected.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
It's my understanding that you must have a path to the air on any line where an AAV is used if it isn't the only thing. The AAV only lets air in, not out. Depending on where you are, the vent may need to let air out, and there has to be a path for it. I'm not sure you have that. Or, I might be all wet!
 