    Greetings! I'm hoping one of you Master Plumbers out there can answer a question for me.

    I'm going through the code book and I understand that it's a no-no to put a sanitary tee on its back. I can understand why this is forbidden if the vertical connection is a drain. A combo would be the solution for that scenario.

    What a don't understand (and maybe my understanding is flawed) is why can't you use a sanitary tee on it's back if the vertical connection is a vent? This would be a crown vent, right? And a crown vent, as long as it's more than 2 pipe size diameters away from a trap, is allowed... am I still correct?

    Thanks in advance for sharing your vast knowledge.

    Regards,
    Marty

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,679

    Default vents

    A crown vent comes off the inverted U bend of an "S" trap and is NEVER permitted. The codes SPECIFY that any fitting below the overflow level of a fixture MUST be assumed to be a drain fitting, not a vent fitting, because it will fill with water when the line is obstructed. In this case you are trying to be logical and the codes are not necessarily logical.

  3. #3

    Default vents

    Quote Originally Posted by hj View Post
    A crown vent comes off the inverted U bend of an "S" trap and is NEVER permitted. The codes SPECIFY that any fitting below the overflow level of a fixture MUST be assumed to be a drain fitting, not a vent fitting, because it will fill with water when the line is obstructed. In this case you are trying to be logical and the codes are not necessarily logical.
    hj,

    Thanks for the reply. LOL! I drive my wife nuts all the time by being logical. I was reading through the code book trying to make sense of some of the rules. Just doing this has increased my respect for plumbers tenfold. You guys really have your work cut out for you.

    Thanks for the explanation. I was wondering what evil might be lurking by putting a sanitary tee on its back.

    Regards,
    Marty

  4. #4
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,216
    Blog Entries
    1

    Default

    I was wondering what evil might be lurking by putting a sanitary tee on its back.
    One explanation I heard was
    Someone may come by later and use a vent for a waste line, so anything below grade must be run with waste, and not vent fittings.

    Of course in plumbing, ask ten inspectors and you will get a variety of answers. Most pretty close.

  5. #5
    Master Plumber nhmaster's Avatar
    Join Date
    Jul 2008
    Location
    S. Maine
    Posts
    2,039

    Default

    IPC allows a san tee to be used for vertical venting as long as it is dry.

  6. #6
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,216
    Blog Entries
    1

    Default

    IPC allows a san tee to be used for vertical venting as long as it is dry.
    UPC requires the use of a santee if it's vertical.

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,679

    Default ipc

    A sanitary tee is cheaper than a combination Y-1/8 bend, that is why the IPC allows it. Many things in the code anticipate future actions, which is why the horizontal run or connection of an individual vent has to be at least 42" above the floor. In case a 36" kitchen sink is eventually connected to it and thus the 6" above the rim will be maintained.

  8. #8
    Master Plumber nhmaster's Avatar
    Join Date
    Jul 2008
    Location
    S. Maine
    Posts
    2,039

    Default

    HJ, are you saying that the IPC guys were bought off by the manufacturers

  9. #9
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,679

    Default Ipc

    NO, the contractors. The UPC and IPC had a merger agreement, but when the IPC contractors learned that they would have to go back to doing good plumbing, they tore up the agreement.

  10. #10
    Plumber patrick88's Avatar
    Join Date
    Sep 2007
    Location
    Webster Ma.
    Posts
    836

    Default

    Quote Originally Posted by hj View Post
    NO, the contractors. The UPC and IPC had a merger agreement, but when the IPC contractors learned that they would have to go back to doing good plumbing, they tore up the agreement.

    LOL That is too funny
    I'm just starting to work with an old friend of mine to bring solar electric and hot water systems, wind turbines, Flex Fuel Boilers, batteries, hydroponic gardening, books, pellet grills and more. Also the parts for DIY installation.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •