Describe inadequate pressure, and the shut downs.
You have a high iron content water and with or without the chlorine, you'll have rust buildup on all the materials in the well; it's normal and not a problem usually unless it blocks up the pump's inlet screen. Or the pellets eat holes in the cable, pump or drop pipe.
The 3-4 check valves, plus the one in or on the pump's outlet probably have a 5 psi cracking pressure. So 3-4 times 5 = a lot of lost pressure. And there is nothing good about having all the extras, you only need the one in/on the pump. The torque arrestor isn't a good thing but won't reduce pressure or cause pump shut downs.
What damage did you find?
At first the Pumptec Plus would stop the pump with a solid amber light indicating "underload". House is two story colonial with three bathrooms, two bathtubs, 2nd floor laundry, kitchen, two outside hose bibs. Gave up having parties here. Water would quit every half hour on us while toilets would flush at the same time people were washing dishes.
Inside:
Check valve and copper pipe to 84 gallon Myers pressure tank set to 38psi.
40/60 Furnas pressure switch.
Pumptec Plus pump protector (installed a year ago). Before that I tried a pressure switch with a low pressure cutoff, but I was downstairs pulling up the lever to start the pump all the time. Even filling a bathtub would be too much. Pump couldn't keep up with the water demand. Took 10 or more minutes to go from 40 to 60.
Whole House filter (Big Blue) with 5 micron Pentek filter (CP5BB) that reduces pressure by 5-7psi. Filter often has black carbon like deposits embedded in it that look to me like Manganese. Not always present. I don't think I have iron in the water. Not 100% sure though. In the summer time especially I know that without any chlorine, a white grease that looks like GoJo hand cleaner will build up and form in the well. 20 years ago when I pulled up the pump we needed a truck with a huge winch to pull the pump up through that stuff. Almost lost everything. Even bleach will dissolve it though.
Hydrogen sulfide odor was addressed with Pot Perm for years until we removed the system (ruined clothes, turned water black, hate the stuff anyway). Chlorine pellets started five years ago (threw them in manually). Worked well for the sulphur. Didn't know it was wreaking havoc in the well with the metal, etc or piling up on the obstructions.
Well:
420 foot depth. Pump set at 390 feet. 4 GPM well recovery. 100 foot or so water column. Coil pipe, 12 Gage (2-wire + Gnd). Originally had a 5 GPM F&W pump with same Franklin 3/4 HP motors as the Goulds has.
*Replaced motors every 7 years because they would burn out. Used to use a 30/50 system with a smaller pressure tank.
Five years ago replaced pump and motor with the Goulds 5 GPM 3/4 HP referenced above. Not sure if it was damaged. I know water dripped out of it when I pulled the pump up. Seemed unusual. Don't know if the check valve at the top has failed or not. Should I rebuild it anyway or get a larger pump? I do have a brand new 1HP motor that I could attach to the Goulds pump. Also, the F&W pump still works AFAIK. Could reuse it.
Looked to be well built and much heavier than the Goulds. Has had six motors over the years. I have the local record for number of times I pulled my well pump. Almost routine.
NOTE: the original pump and all the motors I replaced had no deposits on them. These deposits are something brand new in the last five years. Maybe the chloring reacted with the iron well casing and dripped down into the water corroding the pump and motor outside (and maybe inside?)
So if all the check valves should come out and the torque arrestors and cable guards removed, how does one protect the wire from getting skinned?
And what do you recommend I do so maybe I can get a whopping ten years maybe before I have to pull up my well pump again?
The well driller never wanted to know anything after he drilled. They go for depth here. The deeper the well, the more they get paid. After that it's the homeowner's headache for life and they won't answer any questions unless you want them to come back and make your well even deeper. Then they will drill it to 800 feet in a flash for you.
John