All your reading is continuity.
Your confused on the EARTH and a actual ground, yes I know the NEC does not make it easy, but you have to remember this, that little hole in your receptacles does NOT GO TO THE EARTH. I cannot stress this enough.
This is the scary part, what do you think happens if that pump has a short underground and the breaker does not trip? You end up with a potential shock hazard. Even death. Here is a picture...
An accident waiting to happen.
That will accomplish nothing, it would have to connect back to the service neutral to open the breaker.
Your right, it will conduct electricity, but at a high impedance, which will NEVER open the circuit breaker and clear the fault... this is the danger.
The whole time buddie! Look at it this way, ground rods and other grounding electrodes we install are only for lighting and surges from higher voltage lines, the actual ground wire on a light fixture or receptacle actually tie back to the system neutral, this is what allows the circuit breaker to open during a fault, now sure, we bond the ground rods and such to the system neutral, but it does nothing in terms of protecting us during a fault.
Here is another picture to study, this one actually involves a service without a neutral, but it may help you understand that the earth does nothing in relation to circuit breakers. Picture the motor shown, a well casing with a well pump that has a ground fault.
![]()