    Default Takagi TK2 running at full blast constantly

    I have the book but says nothing about the water heater running at full blast constantly. Filter is clean. It is providing hot water but will not shut down... Please help!

    Thanks!

    Tom

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default heater

    Shut off the water supply and see if it shuts down. If it does you have a hot water leak. If it does not, the heater should be banging and pounding like crazy as it becomes a steam boiler.

  3. #3
    DIY Junior Member
    Join Date
    Aug 2008
    Location
    North Carolina
    Posts
    2

    Default Working normally it seems...

    Thanks hj, I will file that away for future reference. The last time the TK2 ran full blast, it was because the filter was clogged with sand... This time, I cleaned and changed all the filters but still ran full blast...

    It gradually wound down over 30 minutes and is working (apparently) normally now. Not sure what caused the episode. We did have a power hit just before this happened though... Not sure what that would have to do with it.

    Thanks again!

    Tom

  4. #4
    TROJAN WORLDWIDE SALES RP MACPLUMB 777's Avatar
    Join Date
    Aug 2007
    Location
    Houston, Texas, United States
    Posts
    631
    Blog Entries
    1

    Default Water Heater Running Full Blast

    I Could Say Something Funny Like Get Some Rope And Tie It Down Before It Gets Away From You,

    But Really You Need A Licensed Electrician To Wire A Surge Suppressor On That Circuit That The Heater Plugs Into To Keep From Frying The Board ! ! !

    MACPLUMB 777

    E-MAIL
    JERRYMAC@TROJANWORLDWIDE.COM


    35 YEAR MASTER PLUMBER, HEATING, ELECTRIC, DRAINS, FIRE SPRINKLERS, WATER HEATER
    AND BOILERS SINCE JAN, 1989

    281-706-1631 7 DYS A WEEK SALES AND TECH. SUPPORT
    Trojan Worldwide Web Site


     



  5. #5
    Master Plumber master plumber mark's Avatar
    Join Date
    Feb 2005
    Location
    indianapolis indiana - land of the free, home of the brave....
    Posts
    4,244
    Blog Entries
    1

    Talking a quick question?

    If nothing was running in the home, and the unit was
    trying to blast off like a .... F14-Tomcat....for 20 minutes

    how come the t+p valve did not go off and relieve the pressure???

    I would be worried that your unit has sustained
    some pressure related damages to the heat exchanger
    from this episode..


    and I seriousley would change out your t+p valve.

    that had to be one hot puppy........

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default tankless

    One reason is that the majority of tankless heaters, any brand, do not have T&P valves. They have "P" valves because the units are so well controlled that they cannot "run full blast" without a water flow, at least that is what the small print says. I, for one, do not believe it so I always add a T&P valve to the installation. But if it runs for ANY AMOUNT OF TIME without flow the heater WILL start hammering because it it generating steam. THEREFORE, if it is running and not banging there is a flow somewhere.