Thread: Shower make-over

  1. #1

    Default Shower make-over

    Hi folks: This my first post of any kind - ever - so be gentle.
    Project started as a simple re-tiling of a 1970s shower-toilet-vanity. Replace the floor tiles (and install in-floor heating at the same time), replace the wall tile around the shower and toilet area, and replace the floor tile in shower.
    I found the bottom row of wall tiles around the shower just fell off into my hands. The gyproc behind was wet, so I ripped off all the gyproc around the shower to see if there was any damage to the framing (None, thankfully).
    The shower pan is galvanized, 48"x34". I dug out the wet gyproc around the mud+tile slab, which left a 3/4" trough all the way round the inside of the floor pan. There was some free water in the bottom (I wonder why that would not have drained away?)
    The shower never leaked. It's on the 2nd floor with no access from below without major damage to 1st floor ceiling. I want to use the Kerdi membrane on the shower walls.
    Q1: Is it wise to keep the galvanized floor pan? If not, I have to rip out the entire floor and start again?
    Q2: If I can keep it and chip off the existing shower floor tiles, I would want to run the Kerdi membrane down the walls and across the floor pan before installing the new shower floor tiles: Is it possible to tie the Kerdi membrane to the existing shower drain? Or do I have to excavate the old drain and replace it with the Shluter drain? Is that even possible?
    Attached Images Attached Images   

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default pan

    Regarless of what the pan looks like above the shower, I have NEVER seen an older one which was not almost completely rusted through under the tile. And if it is not already so, it will probably be worn out shortly. I would take it out and start over.

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,396

    Default

    That pan is almost certainly flat on the floor. By code, the waterproof layer (the pan, not the tile) must be sloped to the drain. There will be water that gets below the tile and the pan must slope to the drain to allow it to flow out. While it doesn't leak (yet), your pan is not built properly and should be removed and replaced.

    Kerdi is only designed as a system...walls, pan, drain. It would not be warranteed unless you use the whole system (note, you do not need to use their preformed pan as part of the system, but can if it fits your needs). There isn't a good way to attach Kerdi to a conventional drain.

    Tear it out!

    Read up on proper shower construction at www.johnbridge.com.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4

    Default Shower make-over

    Thanks JADNASHUA and HJ for your replies.
    Great advice, even though you confirmed my worst fear - having to rip out the entire shower floor. What started as a simple re-tiling project...well, you know how that goes. I'd rather do it right, though, so I will rip out the shower floor. And you are correct: The pan is flat to the floor. No wonder water collected around the edges.

    Q1: Am I best to chip away at the edges and work my way towards the drain, or is it possible to excavate the drain, cut it and then lift out the entire floor pan? It would weigh a couple hundred pounds I imagine, so I'm guessing that's not the way.

    In the same project, I have a question about a toilet flange. Along with the old floor tiles I have taken up the old 5/16" ply subfloor, except around the toilet flange which is still sitting on the old tiles-and-subfloor. I will be raising the height of the floor by almost an inch (thicker subfloor plus in-floor heating). The existing flange, by its color, seems to be brass or bronze, soldered (I'm guessing) to the 3" copper waste pipe. The "advisor" at our local building supply center suggested I leave the existing flange in place and insert a 4"x3" ABS flange into it. This would add 5/8" to the total flange height, not quite as much as the increase in floor height (13/16"). I bought one and it fits nice and tight into the existing flange. The "advisor" suggested I only need to silicone it to seal them together. He was cagey when I asked if this would meet code.
    Q2: What do you think of the idea of adding a second flange on top of the first? If not, is my only alternative to cut the copper drain to get the old flange off, and then use a flex coupling to install a new plastic riser and flange?

  5. #5
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    I'll add the third strike... It's outta here!
    The John Bridge site that Jadnashua linked will be a most valuable resource to you on your project. There is a forum there as well.

  6. #6
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,396

    Default

    It might be possible to remove the existing flange and reuse it - the coupling part may be deep enough.

    If you have access from below, you could cut it off, then add on a riser and new flange properly installed and supported by the new floor.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  7. #7
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    Its funny how smockman suggests repairs like that then when asked about code he gets a little cagey.

  8. #8

    Default Shower make-over

    As promised, and following your excellent advice, I removed the shower floor. After messing around with a hammer and chisel for a couple of hours, I discovered a short-cut: I chipped off a row of tiles and drilled a row of holes with a masonry bit, levered up the slab just a fraction and then hit it with a mini sledge, and it cleaved along the line of holes. 15 minutes and it was done.

    Q: How do I remove the pan now? The drain has a flange at the junction with the pan. There are three hex bolt heads through the flange and pan (one is visible in the picture). Even if I undo the bolts, and then unscrew the flange, I can't get it off over the drain because that mushrooms out at the top. So, do I cut the pan?
    Attached Images Attached Images    

  9. #9
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,396

    Default

    The drain should separate when you get the bolts out. Then, it's easy. It looks to me you'll need to replace the drain anyways, so you could cut it off, too.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  10. #10

    Default Shower make-over

    Thanks, JADNASHUA: The drain did indeed come apart after the bolts came out. I am amazed to see that there's no gasket or seal between the two halves of the drain and the shower pan.
    The 5/16" ply subfloor is coming off next. One of the attached photos shows some water damage in a small area along the back wall, but I am replacing all the subfloor in the whole room anyway with 1/2" ext.grade ply.

    All the drains and vents in the house are copper: In the case of this shower drain, it's 2".
    Q1: If I have to cut off the existing bottom part of the drain, I assume it's easiest to open the floor and cut the horizontal pipe after the trap?

    Q2: Hacksaw, or is there a better way?

    Q3: Then install flex coupling and new plastic trap and riser, ready to receive the Schluter drain: Would that be the order of the day?
    Attached Images Attached Images    

  11. #11
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,396

    Default

    You don't want a flexible connector there! Use a no-hub. This is a neoprene rubber sleeve with a metal shroud and a couple of hose clamps. You may have to pick this up at a plumbing store since the ones usually available at a big box store are designed for CI to CI or pvc to pvc...the OD of copper is smaller and yes, they do make one for this.

    You may want to take this opportunity to ensure the new drain and trap are exactly centered within the area of the shower. While not absolutely essential, it does make layout and building it easier.

    If you haven't been over to www.johnbridge.com, building it back up to tile is covered very well there.

    Make SURE that the riser from the trap is perfectly plumb. The drain must sit on there and be level, or you'll have big pains.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  12. #12

    Default Shower make-over

    Got it.
    I've seen the coupling that you mention so I'll be sure the get the correct kind.

    Is cutting the copper pipe a simple hacksaw job, or a power recip saw, or what?

  13. #13
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,396

    Default

    Hack saw, sawsall, or if you have one big enough (probably not) a pipe cutter. Clean off the burrs. The harder part is getting it fairly square - a pipe cutter almost guarantees that, but probably not enough room to swing it anyways.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  14. #14

    Default Shower make-over

    Shower drain first:
    There's no way to remove the trap because the junctions are all up against one another (photo) but I have enough height that I can cut the riser, install a coupling, and have a couple of inches left to mate with the Kerdi drain. It's too cramped to get the power saw in there so I'll have to hacksaw the copper. Any other suggestions?

    Toilet drain:
    Again, the vent junction limits the options. I've measured and drawn the installation and, with the coupling and new ABS bits, the height is OK. But, if I cut close enough to the vent junction to leave a stub of copper for the coupling to connect with, the new installation puts me 3/4" over laterally from the present position (off to the right as you look at the photo). I don't believe that would be noticeable (or would it?). I've seen an offset closet flange at our local HD: What do you think of that idea? It could bring the flange back into position, no? Are offsets more prone to blockage?
    Attached Images Attached Images   

  15. #15
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    You want to remove those 2 90's after the trap up against the joist. They make an extra deep trap that can result in slow drainage.

    As JAD Nashua stated remove the burrs from the copper... We don't want any hair catching going on!

    How it that shower vented? In your pictures I don't see any vent. There should be one before it elbows down to the toilet line.