    Default Venting a gas water heater

    hope this is the right section for this question.
    I am changing out an electric water heater for 2 propane fired models.
    1 for the domestic hot water usage, and a 2nd to run the radiant heat system I am putting in.
    The location of the tanks does not allow a vent pipe to go straight up to the roof, right now I'm looking at running a vent pipe about 11feet horizontally to an exterior wall then up the side of the house to roof level.
    Does this sound right?

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,448

    Default

    To maintain a decent draft, there are limits on how far you can go...it depends on the manufacturer. I'd prefer maybe a powervent in this situation that vented out the sidewall. ALso, keep in mind, unless your BTU requirements are fairly small, a WH may not be able to supply your needs. The type of heat loops (radiators, in-floor, panels, etc) each require different temps. Some require higher than a typical WH can provide. The average WH probably won't have the reliability of a boiler, either. Today's modulating HE boilers are in the mid-90% efficiency range and can easily provide all the DHW you want more efficiently than a WH.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    With all due respect, I think you should get a professional to handle this installation. Not only does the venting have to be done right, the question on having the right kind of heater for the radiant heating needs to be addressed. You can get some pretty sound advice here, but it really needs to have a professional on site.

  4. #4
    DIY Junior Member zenn068's Avatar
    Join Date
    Jan 2008
    Location
    New York
    Posts
    11

    Default thanks for the infi,

    should point out that the 2nd water heater is a radiant heat specific type.

  5. #5
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    The installation manual for your water heater will have specific instructions on allowed venting. For example, it will be required to run a certain minimum distance vertical before turning horizontal. There will be limits on # of elbows, and there will be a minimum ratio of vertical pipe length to horizontal pipe length.

    Most manufacturers have the manuals available on line to look at.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,687

    Default vent

    Unless the outside vertical pipe is insulated, heat loss will prevent a normal draft from forming and you WILL get carbon monoxide fumes in the building.