If I have a circuit with 14 guage wire and a 15 amp breaker, can I tee off or extend that circuit using 12 guage wire? It seems that as long as the breaker is sized at 15 amps, the smallest wire size (14) would be adequately protected, and the 12 would be over protected.

Of course that's just me. I have someone telling me that you can never do such a thing. So the question is:

1. is it a code violation?
2. if it is, what is the theory behind it.

Thanks
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
OK, this is a plumber talking, not an electrician. I have just enough knowledge about electricity and codes to be dangerous, as they say!

I don't think it would be a code violation, as long as you did not run that 12 guage to a 20 amp receptacle.

Let's wait for speedey or bob for your official answer. The rationale for NOT doing it, code or not, would be that in the future, someone might just see that 12ga. somewhere, and assume that they could upgrade the BREAKER to 20 amp. That would be a problem!
 

Billy_Bob

In the Trades
Messages
419
Reaction score
0
Points
0
No, you can not mix wire sizes on the same branch circuit.

The reason is someone may install a larger breaker thinking that all the wire in that circuit is the larger size.

In your case, some future do-it-yourself owner of your home may measure the wire size at the outlet, then assume all the wire is that size, then not even look at the wire size in the panel and then install a larger breaker.

Best that everything be straight forward and consistent.

Also if you sell your home in the future, a home inspector might catch this. If they see some things like this not done to code, then they will look very closely at everything else, then report these things to the potential buyer. Might kill the sale!
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
wire

Rational reply, but;
1. What inspector is going to remove an outlet to check wire sizes, especially since he would have to remove ALL of them to verify any discrepencies.
2. If the user knows enough to check an outlet for wire size, and is smart enough to find which breaker feeds it, the assumption would be that he is also smart enough to recognize the breaker wire size.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
No, you can not mix wire sizes on the same branch circuit.

The reason is someone may install a larger breaker thinking that all the wire in that circuit is the larger size.
This is incorrect. Larger sized conductors are installed all the time to confiscate for voltage drop in such things as well pumps and the like.

In your case, some future do-it-yourself owner of your home may measure the wire size at the outlet, then assume all the wire is that size, then not even look at the wire size in the panel and then install a larger breaker.
In this case it would be the idiot that was doing the work at that time that would be making the mistake not the original installation.

Best that everything be straight forward and consistent.
So how would you wire a well pump that is 200 feet in the ground and 200 feet away from the house?

Also if you sell your home in the future, a home inspector might catch this. If they see some things like this not done to code, then they will look very closely at everything else, then report these things to the potential buyer. Might kill the sale!
If a Home Inspector wrote an installation up as being incorrect as outlined in the original post then the Home Inspector should be reported as not knowing how to properly do his job.

The bottom line is the installation as outlined is perfectly legal and compliant.
 

Billy_Bob

In the Trades
Messages
419
Reaction score
0
Points
0
Rational reply, but;
1. What inspector is going to remove an outlet to check wire sizes, especially since he would have to remove ALL of them to verify any discrepencies.
2. If the user knows enough to check an outlet for wire size, and is smart enough to find which breaker feeds it, the assumption would be that he is also smart enough to recognize the breaker wire size.

Actually home inspectors find all sorts of "handiwork" done by do-it-your-selfers all the time. Some of them do remove outlet covers to peek inside, although mostly they are looking for a two wire no ground going to a 3 prong outlet with a jumper from neutral to ground on the outlet (a no no). Or no box installed (outlet just placed in wall).

So far as using larger wire for the entire circuit, that is ok. It is MIXING wire sizes on the same branch circuit which is the problem.

As to people doing dumb things, you would not believe what people can do to their electrical wiring...

Here is one from a home inspector's forum where someone replaced the fuses with copper pipe!
http://www.inspectorsjournal.com/Forum/topic.asp?TOPIC_ID=7705

Here is one from the same forum where a home inspector found a neutral to ground wire on an outlet (clue was he removed the breaker panel cover and noticed there were no ground wires)...
http://www.inspectorsjournal.com/Forum/topic.asp?TOPIC_ID=7501
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
No, you can not mix wire sizes on the same branch circuit.

. . . . .

So far as using larger wire for the entire circuit, that is ok. It is MIXING wire sizes on the same branch circuit which is the problem.

Billy_Bob; please cite the National Electrical Code paragraph to support the statements from two of your posts as quoted above; or acknowledge that there is no code to cite.
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
From the following link "You cannot mix different wire sizes on the same branch circuit."

http://www.co.jefferson.co.us/building/building_T45_R9.htm

Other than the above, I'm not going to argue. Just ask your local electrical inspector and see what he says.
Other than the fact that that article is FLAT WRONG. It says it is quoting from the 2005 NEC, but they are wrong and there is no substantiation for this comment.
You can't pull up some local building dept web site that is providing incorrect information and call it fact. That site is half code citation and half interpretation.

Find it in the 2005 NEC and THEN post it. It's OK, we'll wait. :rolleyes:

Your local inspector can say all he wants, but unless there is a written amendment they have no grounds to enforce their requests.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
From the following link "You cannot mix different wire sizes on the same branch circuit."

http://www.co.jefferson.co.us/building/building_T45_R9.htm

Other than the above, I'm not going to argue. Just ask your local electrical inspector and see what he says.


It might be a good idea for someone to contact the Jefferson County Co. Building Department and let them know that their site is in direct violation of the 2008 NEC which they claim to have adopted.

They are allowed to adopt rules that are more stringent than the NEC but they are out of bounds by adopting the NEC and then modifying the rules to a less stringent format.

As outlined in their web page Copper #8 NM cable is not good for 50 amps but as outlined in 334.80 must be sized from the 60 degree column as is only good for 40 amps.

#6 copper NM cable posted on their website is good for 65 amps but again as outlined in 334.80 it is only good for 55 amps.

They have also posted #8 aluminum as 40 and #6 as 50 but in the 2008 code it clearly states in 338.10(B)(4) SE type cable must comply with Part II of 334 which contains 334.80 again sending the installer back to the 60 degree column.

I think that someone should let them know that the author of this site is NOT qualified to be making such statements and should be fired immediately before someone gets hurt making such foolish installations.
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
From the following link "You cannot mix different wire sizes on the same branch circuit."

http://www.co.jefferson.co.us/building/building_T45_R9.htm

Other than the above, I'm not going to argue. Just ask your local electrical inspector and see what he says.

You have found another example of some code enforcement official talking through his hat. The unreliability of the Jefferson County Wiring Guide is demonstrated by the fact that they identify a higher Ampacity of #8 and #6 NM cable than is permitted by the Code.

The table in the wiring guide says 50 and 65 Amps for #8 and #6 copper NM. (The table won't reproduce here). I don't recall ever seeing #8 and #6 NM.

NEC 334.80 requires that ampacity of NM cable be based on the 60 C rating, notwithstanding the 90 C rating of the conductors in the cable.

That means that the #8 and #6 NM must be provided with overcurrent protection not exceeding 40 and 55 Amps respectively.

The statement that if you begin with #12 you must use it throughout has some rational basis but is not required by any code that I am aware of.
 

Johnny C

Electrician
Messages
23
Reaction score
0
Points
0
Location
Mass. & now Virginia Beach, VA
Wire Size Quest.

The NEC does NOT prohibit properly connecting a number 12 awg Cu conductor to a number 14 awg Cu conductor that has overcurrent protection rated at 15 amperes. This is no different than connecting number 12 awg Cu directly to a 15 ampere overcurrent device. In some instances a conductor sized based in accordance with the load and overcurrent device might terminate in a junction box, and due to a lengthy circuit or feeder, the conductor size is increased to compensate for voltage drop. However, due to the terminal size, the larger conductor would not fit in the terminal, and the smaller size conductor was used to connect to the fuse or CB.
 