Vent Issues

Users who are viewing this thread

bzack32

New Member
Messages
1
Reaction score
0
Points
0
I am installing a Zoeller Ejecter pump system for a basement bath. I need to tap into my 3in copper vent and connect to a 2 in pvc pipe. Any ideas, because the flexible rubber tees seem too large for the copper. I think they are designeg for cast or pvc.
 
Last edited:

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
Cut a tee into the 3" using Fernco Proflex Couplings # 3001-33
http://www.fernco.com/proflex.asp

proflex.gif


This vent must be tied in above any drains on the 3", It must be 6" above the flood rim of any fixture that drains into the 3".
 