Lake pump pressure

Users who are viewing this thread

dmarple

New Member
Messages
9
Reaction score
0
Points
0
Hi Folks

I am running my sprinkler system with a lake pump. I have noticed recently that the pressure/flow in the system drops after the pump has been on for a while - say 2- 3 hours. Until then it operates normally. The pump is 5 feet above the water surface. The foot valve is 4 feet below the surface. I have checked the foot valve for obvious things that might restrict flow and have not found anything. It is 4 years old though and I suspect it may be the problem. Any thoughts ?

Thanks
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
Is it possible that the zone that comes on later in the cycle has more heads or a leak in the distribution system that demands greater flow? That would cause the pump to deliver less pressure.
 

dmarple

New Member
Messages
9
Reaction score
0
Points
0
I don't think that is it as it seems to happen no matter what what zone sequence is running.

As an example I had it set to run at 4 am today. When I went out ther apx 6:30 it was running zone 5 but hardly enough pressure to pop the sprinkler heads. I checked the pump/motor and its sounded normal and was not overheating. I shut it off for half an hour. I restarted zone 5 and it worked fine throughout the rest of the program.

Thanks
 

Southern Man

DIY Hillbilly
Messages
525
Reaction score
0
Points
0
Location
North Carolina
It sounds to me that the motor is over heating. You should check the voltage at the motor while off, then while running. If there is significant drop (more that 2 or 3%) then your feed wire is too small. Most motors don't like voltages less than 115 or so, and prefer 120.
 

Speedbump

Active Member
Messages
4,511
Reaction score
12
Points
38
Location
Riverview, Fl.
If your only using a Footvalve for a Lake Strainer, you can assume that every leaf that comes in the vicinity of the Footvalve will try it's best to get sucked up against the screen.

You may need a real Lake Strainer.

bob...
 

dmarple

New Member
Messages
9
Reaction score
0
Points
0
For some reaon my Reply dropped off. If this is a repeat please forgive me.

The motor is 2 HP and is supposed to be hooked up to 240 V. 240 is out there but I neve really checked to see if it is wired correctly. It does run hot or it seems hot to me. Not so hot That I can't put my hand on it but hot. Of course its in the 90's in Texas. Would it even be possible to Start and run a 2HP motor on 120 V ?

It sounds like I need to invest in the Strainer irregardless of the othe issues.

Thanks for everyone's replies.
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
You may have low voltage to the motor... But Not That Low!:eek:
Measure it if you have concerns.
 

dmarple

New Member
Messages
9
Reaction score
0
Points
0
Thanks - will do, Just thought of somehting else, If it were the foot valve or something else obstructing the suction wouldn't that show up on my suction pressure ? What would it do, raise the pressure ?
 

Speedbump

Active Member
Messages
4,511
Reaction score
12
Points
38
Location
Riverview, Fl.
Suction - Pressure? It's either one or the other, they are opposites. If you had a Vacuum Gauge in the Suction line, you would probably see a very high reading, like 28 inches of Vacuum. But while pumping lots of water, there is always going to be a rather high amount of Vacuum on that line.

bob...
 