    Default Programmed versus manual activation

    One station in our sprinkler system is having a problem I've never encountered before. It works perfectly when manually opened at the local vault box, but when activated by the automatically timed control box there is significantly less pressure, such that the pop ups do not rise up much. Any suggestions will be much appreciated.

  2. #2
    Sprinkler Guy Wet_Boots's Avatar
    Join Date
    Mar 2007
    Location
    Metro NYC
    Posts
    798

    Default

    Make and model of valve? (or a photo)

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,615

    Default va;ve

    The manual and automatic methods operate differently. If the automatic method does not "dump" water fast enough, or if it is damaged internally so the water is being replenished as it is dumped, then it will not open entirely. Manual operation usually can overcome any bypassing internal leakage and open all the way. You may have a bad diaphragm, weak solenoid, restricted solenoid water passages, etc.

  4. #4
    DIY Senior Member Joerg's Avatar
    Join Date
    Oct 2004
    Location
    Califonia
    Posts
    138

    Default

    Or the solenoid plunger can't fully retract anymore because rust or crud has accumulated in the shaft. I'd take it off and look.

    Regards, Joerg.