Thread: PVC - Copper Pipe Joint

  1. #1

    Unhappy PVC - Copper Pipe Joint

    The PVC pipe broke at the joint between the 1" supply line and the primary valve right at the end of the threaded copper pipe. Do I replace the threaded copper end or how do you remove the threaded pvc from the copper?

  2. #2
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,244

    Default

    Is the threaded copper a female adapter? If so, it might quicker and easier just to cut the adapter off, sweat a new one on and not even attempt to remove the broken PVC. To remove it, you'd have to make a couple of cuts in the PVC then pry the pieces out. You'd mess the copper threads up to a certain extent doing this which could make it difficult to get a leak free connection, and you'd not make very good wages saving the cost of a new adapter.

  3. #3

    Red face New Adapter

    The copper fitting is female. So just grab a torch, take it off and add a new one? Any special considerations for solder, gas ??

  4. #4
    In the Trades Bob NH's Avatar
    Join Date
    Oct 2005
    Location
    New Hampshire
    Posts
    3,307

    Default

    Quote Originally Posted by jgalway View Post
    The copper fitting is female. So just grab a torch, take it off and add a new one? Any special considerations for solder, gas ??
    95/5 tin/antimony solder, Oatey No. 95 tinning flux, and a propane torch will work fine.

    Very good cleaning is important.

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,602

    Default joint

    Leave the copper alone, and remove the plastic piece from the female adapter. There are several pipe removers that will work.

  6. #6
    Sprinkler Guy Wet_Boots's Avatar
    Join Date
    Mar 2007
    Location
    Metro NYC
    Posts
    798

    Default

    You can always melt the remaining PVC and pry it out of the fitting.

  7. #7

    Default

    Used the torch to remove the female fitting. It came off easily and so did the PVC which was quite soft. Reattached the fitting. Will be testing the system today. Thanks

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,602

    Default pvc

    How did you reconnect the pvc to the copper? Not with another male PVC adapter, I hope.

  9. #9
    DIY Senior Member Mr_Pike's Avatar
    Join Date
    Jun 2007
    Location
    Nebraska
    Posts
    136

    Default

    I quit using PVC male adapters a long time ago. If you need to make a connection to female Iron or copper pipe. Cut a Pipe Nipple in half and use a coupling to join half to the PVC. You will have a joint that is twice a strong...

    A PVC male adapter might as well be perforated at the bottom the the threads.