Howdy,

I am doing a new toilet installation. The 4" waste pipe will drop from the toilet flange straight down a couple of feet, then through a 90 degree bend, then has a few feet of horizontal (on a slope of course!) run to the stack.

I have a 2" vent ready in the vicinity, and will connect the vent to the waste pipe with a 4x4x2 sanitary TEE.

Question: I could install the TEE either in the vertical drop pipe, above the bend, or immediately after the bend in the horizontal section of the waste pipe.

Is either one better? I think the vertical option is best, as it puts the entry of the vent air as close to the toilet as possible.

Many thanks for any advice!

Dayster
 

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
Mechanically, you do not need to vent that line at all since there is absolutely no way a toilet can ever release enough effluent rapidly enough to fill a 4" line and siphon its own trap. As long as the plumbing below the toilet (4") is larger than the opening in the bottom of the toilet (less than 3"), no additional venting is mechanically necessary. Nevertheless, I would go with your vertical option unless its installation would be extremely difficult.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,458
Points
113
Location
Bothell, Washington
Website
terrylove.com
You can use the vertical postition or the horizontal. Either way, I would consider a wye fitting for the vent. If the vent is within six feet, you are fine.
Venting the toilet helps to prevent other fixtures from siphoning dry.
 

dayster

New Member
Messages
23
Reaction score
0
Points
1
Location
Vancouver, BC
You can use the vertical postition or the horizontal. Either way, I would consider a wye fitting for the vent. If the vent is within six feet, you are fine.
Venting the toilet helps to prevent other fixtures from siphoning dry.