Ked, the other day you posted the following:
I asked you to please cite the NEC Article where this prohibition appears. Since you have not returned to the forum since I made that request I decided to post this as a new topic so my question would not get lost in the other topic.
I am quite aware of several provisions that must be followed when circuits of different voltages are in the same raceway but I am not familiar with any prohibition such as you wrote.
NEC prohibits installing any below 50 v. wiring in conduit with 120 v. or higher wiring, but you did not want to do that anyway.
I asked you to please cite the NEC Article where this prohibition appears. Since you have not returned to the forum since I made that request I decided to post this as a new topic so my question would not get lost in the other topic.
I am quite aware of several provisions that must be followed when circuits of different voltages are in the same raceway but I am not familiar with any prohibition such as you wrote.