Page 1 of 2 12 LastLast
Results 1 to 15 of 22
Thread: Problem with Takagi & Radiant Heat &Domestic Hot Water
    Default Problem with Takagi & Radiant Heat &Domestic Hot Water
    Last year I remodeled my home and installed plex tubing throughout my 2 unit building. Upon the advise from a company back in Vemont, I installed a Takagi Jr. to run the radiant heat and domestic hot water supply.
    The downstairs unit works like a charm with no problems (although I did have to remove all flow restrictors from faucets and shower/bath tub).
    The big problem is with the upstairs unit. Back in February, the domestic hot water seems only to work when the radiant system is turned on and burning. I called Takagi twice and they sent 2 repairmen but they looked overwhelmed by the system and said the system works fine and they could not find anything wrong with the water heater.
    I shut off water to the tankless and turned on the hot water to a facet upstairs and found there was no cross water line. The company who sold me the pre-assembled board is going to send me a new one provided I do not ask them for any more technical advise (which by the way, I spend nearly $1500 on all new faucets and replacing the shower unit).
    I am now in a situation where everyone is pointing fingers at each other. Takagi says something is wrong with the plumbing, Vermont Company is saying its the Takagi, and the plumber saying there is no cross water lines.
    Frustrated, I am ready to let the Takagi Jr. take care of the radiant heating supply and I will install back a traditional hot water tank.
    I was so frustrated that I even offered to buy an airline ticket for an employee of the Vermont company that sold me the system to come out West. Their response was take a new set up but don't call us anymore.
    My tenants have been very patient but I want to give it one last try to fix the system. It works so well down stairs. I am going to swap machines to see if this helps and prove once and for all if it is indeed the heater.
    Could I have the wrong size Takagi? The upstairs has 2 bathrooms, kitchen, and washer.
    How many BTU does the thing draw? What's its rated gallons/minute? I assume you have a heat exchanger for the radiant heat, as you wouldn't want to run potable water through all those lines.
    What is the heat load on the house? In other words, how much heat do you need in your boiler (heater)? Does the system operate with priority zones? If the priority scheme is not set up properly, (i.e., when you call for hot water for washing, showering, etc.), if it is still providing heat to the heat exchangers for space heating, the potable water will never get hot enough. It needs to bypass the heat exchangers. If the zone valve or pump is still running, you won't get any hot water for the shower. Both units need to restrict flow to the heat exchanger(s). A diagram of what you have might be useful.
    It could be as simple as a stuck or improperly positioned check valve, zone valve, or pump.
    I'm not a fan of using a potable water heater (tankless or conventional) for space heating.
    Feb 2005
    Talking install the tank...
    you installed this in RENTAL PROPERTY????
    is that correct, you mentioned that your tennants have been very patient???
    so you are having to constantly go over and fool around at this property to figure out what is going on??
    I dont think that this was a good idea in the first place becasue of the demands that tennants usually make on the lanndlord anwway
    I suggest you install a 50 gallon gas heater for their domestic needs,
    and cross your fingers and hope the takagi can give you trouble free service on the radiant heat side of this system or some cold winter day the tennants will be screaming for heat..
    good luck
    DIY Senior Member houptee's Avatar
    Aug 2008
    Monmouth County, NJ
    Default Takagi for heating
    I would like to see some pics of how this Takagi is piped for your heating system, and what controls are being used etc.
    I want to do the same thing but not have system supply domestic hot water, just run the cast iron radiators after I repipe with pex and home run it all back to manifold setup.
    Any advice on that from anyone?
    Feb 2005
    Talking go for it...
    have never heard back from that first fellow to even
    find out what has transpired.....
    to do something like he did you got to be a glutton for punishment
    as long as it dont break down on the coldest day of the winter
    you might get by ok....
    good luck
    Default Takagi piece of junk
    I too have a problem with my water TAKAGI water heater. We bought a T_K2. It lasted about four years then the dreaded number 12 error code comes up. Takagi tech support was very unknowledgeable. We sand and dismantle, and clean and spray, still nothing. They then blame it on the gas pressure. Gas company came out four times, to make us happy, they changed out the regulator, the meter, and measured the pressure. Nothing is wrong except the Takagi system. Now the company blamed it on installation. It was installed and inspected, and working for four years. hmmmm. They will not negotiate or work with us. Offered us an upgrade at an outrageous price, said I could pick one up cheaper on the internet. Whoa, what do you mean cheaper, if you don't buy it from us then we won't honor the warranty even though it's a brand new unit from an internet store..not ****..said the TAKAGI rep. Not only that but they called back and harrass me about the name of the internet company that sell their product cheaper then them. I have no hot water, my daughter is crying, and they worry about someone undercut them? We have gone back to the tank system, phew...hot water...a word of advise, tankless system doesn't really save energy, water pressure weak if you use hot water at more than one faucet, and when it's time for repair, don't call a plumber because all they know how to do is install. If you really want to go with tankless, stay away from TAKAGI...try Rheem, at least GE stand behind their products.
    Master Plumber nhmaster's Avatar
    Jul 2008
    S. Maine
    Quote Originally Posted by tamileetx View Post
    These sorts of problems and complaints will begin to multiply as more and more of this junk is foisted on a market hungry to do the green thing. It's amazing how we never seem to learn from the mistakes of the past, a la ELM Aquastar and Paloma Pak. Very similar units with all the same technical problems as the current incarnations.
    Dec 2006
    There's that "company in Vermont" again. What a bunch of... I swear, those guys are doing more to turn people off of radiant, and tankless, than anyone else in the country. Poop-heads.
    Potable hot water shouldn't be combined with your radiant, in the first place; it's just a bad design idea in the first place.
    And Tagakis aren't as good as Noritz (but whatever you do, stay away from Bosch tankless, they're even worse).
    Try heatinghelp.com, the guys there will want more detailed info, but will help you solve it, they're experts on hydronic heating.
    Master Plumber Mark:
    do not hit your thumb...
    __________________
    Aug 2008
    Monmouth County, NJ
    Default Takagi TK Jr working great for me
    I have 3 TK Jr's tankless for domestic hot water in a 3 family home.
    They are working fine for 2+ yrs. Each has one bathroom/kithen and washer. No problems at all.
    There is a screen on the inlet of the cold water fitting maybe you can check it for debris if pressure is not good.
    My gas bill went down $700 a year by installing these in place of the 3 sep 40 gal tank heaters that were approx 8 yrs old.
    DIY Junior Member techsavy's Avatar
    Sep 2009
    ontario
    So your Takagi worked great for you for four straight years without any problems. I am assuming you didn't maiuntain it throughout those four years. You probably also have the unit installed in a laundry room. This type of installation would cause the burners to slowly plugg up and lead to the error code that you described. This is not the fault of the unit. A simple solution would be to remove the burner and use compressed air to blow the particles that have built up inside of the burner over the years. You should also check your heat exchanger finns at this point to see if that is blocked as well. If it is, blow that out as well and that should take care of the problem. If it does not, then your overheat cut-off fuse may simply be weak and needs to be replaced. This is also a problem that could be caused by blockage in the burner or heat exchanger coils/fins.
    Good Luck with your unit, but it is not the fault of the water heater. Takagi tankless have an excellent repulation and only poor installations for the most part give tankless water heaters in general a bad reputation.
    Sep 2009
    ontario
    Quote Originally Posted by siammurph View Post
    Could it be that the upstairs is connected in series with the recirculation pump that runs the heating application? If this is the case, your upstairs fixture simply will not operate unless the pump is running. Take a look at the set-up and see if there is a pump located before the line that tees off to the fixture that you are speaking about.
    If you can post a diagram of the system, I would be able to identify your problem.
    Sep 2009
    ontario
    Quote Originally Posted by nhmaster View Post
    He used his water heater for four years, not problems. Didn't maintain it, and now it doesn't work any more. Okay, lets blame it on the water heater why don't we.
    Fact of the matter is everything needs maintenance. Unfortunately, the people that were sent to this guy didn't know about the units and the installers did not take the time to learn enough about the product prior to installing it. Tankless have been in other parts of the world for over 60 years and no one is complaining about them. If they were horrible, why is the technology still alive. Tell anyone from Europe that you have a storage tank type water heater and they will laugh at you.
    As for GE and Rheem, good luck with them, since they don't even manufacture their own products. If you really truly want a good tankless water heater, do your research and make sure that you purchase a Japanese model as they have the most stringent design criteria.
    Feb 2005
    Talking words to live by
    this week, I have had 3 people call me about their tankelss water heaters..
    all 3 were Bosches, all three had broken down... with no one in town wanting to work on them
    It kind of Reminded me of the story of the 3 little pigs....and I was the Big Bad Wolf......
    Piggey #1 the first lady was rather huffey with me , telling me how she was saveing the palnet, and we all got to do our part.. and she whoud find someone else more competent to repair her unit in the yellow pages.....
    I was not going to explain anything to , and her mind was made up.
    I would love to hear how that search went and the cost of the
    to her 6 year old Bosch tankless.
    Piggey #2 This fellow decided to install his Bosch into his regular furnace flu pipe
    going up the center of his home... ........oh my goodness, thats a no..no........
    I told him that he might burn his home down that
    way, because his metal chimmney was not designed or rated for the intence heat
    that the tankless would put out,
    I dont think he wanted to hear what I had to say
    I was being too blunt explaining to him that
    that his house might burn down.....
    Piggey #3 I did not even waste my time trying to help her,
    I figured what was the use....its all gonna fall on deaf ears..
    they are all convinced that
    I am the big bad wolf........
    Quote Originally Posted by houptee View Post
    Same with all my neighbors who has had the tankless for years. DANG!
    Journeyman Plumber jdgoodman's Avatar
    Sep 2009
    Seattle
    99* Of Takagi calls i go on i find a reason they are not functioning. Its always the same story, Bad venting, gas issues, poor placement or just no maintenance. I thought i was a tankless pro until i went to Takagi's plant in California for their training class. Needless to say i discovered i was far from it. People blame the units but in most cases it is the installer or the owner.
  1. Takagi Jr Radiant Heat Issue
    By kjensen in forum Tankless Water Heater Forum
    Last Post: 12-24-2010, 10:31 AM
  2. 1 Boiler for Both Radiant Heat and Hot Water Possible?
    By cloves in forum HVAC Heating & Cooling
    Last Post: 02-26-2010, 01:33 PM
  3. Problem with Takagi & Radiant Heat &Domestic Hot Water
    By siammurph in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Last Post: 12-20-2008, 12:24 PM
  4. Best hot water solution for radiant floor plus domestic hot water?
    By Montalvo in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Last Post: 07-03-2007, 09:05 AM
  5. tankless water heater for radiant heat
    By pmayer in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Last Post: 09-10-2006, 05:38 PM
