Thread: Cause of Taco wate circulator noise?

  1. #1
    DIY Junior Member goshenplumber's Avatar
    Join Date
    Mar 2007
    Location
    WV
    Posts
    23

    Default Cause of Taco wate circulator noise?

    I have hot water baseboard heat. When the water circulator is running (and the sound is not masked by the furnace burner noise), there is a noticeable humming / vibration that can be heard at the baseboard heaters. The noise is not from vibration within the baseboards. The noise seems to be coming from the Taco water circulator (model 007-F5) with the noise being transmitted through the heating piping. Note that this noise is not the noise one hears when there are air bubbles in the circulating water. My plans are to replace the circulator cartridge thinking that the cartridge bearings are going bad and that is the noise source.

    However first I tried an experiment. After a heating cycle, when the furnace water temperature dropped below 100, I popped the boiler relief valve. A large puff of air escaped plus about two quarts of water. With the water intake valve open, I allowed the furnace pressure to build back up to its static pressure of 12psi. I then turned the furnace on. The noise was gone!!

    Why did this experiment work? Am I missing something here?

    Thank you.

  2. #2
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,681

    Default

    I'm not a boilerman but will put forth a theory... perhaps the air was causing some cavitation in the pump.

  3. #3
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    No boiler guy either, but they should have an automatic air release valve. Your taco should have water lubed bearings meaning they last about forever.

  4. #4
    Master Hot Water Mpls,MN BadgerBoilerMN's Avatar
    Join Date
    Mar 2011
    Location
    Minneapolis
    Posts
    285

    Default

    Air in a boiler or baseboard is bad, very bad. Getting it out and keeping it out will increase comfort and system life while decreasing the fuel bill. Look the the near piping and air elimination devices.

Similar Threads

  1. Taco 006 BC4 Circulator pump running 24/7?
    By scottall in forum Water Heater Forum, Tanks
    Replies: 2
    Last Post: 03-18-2010, 07:42 AM
  2. Taco circulator info/advice sought
    By Mainuh in forum HVAC Heating & Cooling
    Replies: 5
    Last Post: 11-26-2007, 08:52 AM
  3. taco circulator wiring
    By litemine in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 11-25-2007, 03:28 PM
  4. Taco Flo check circulator pump
    By MarkHash in forum HVAC Heating & Cooling
    Replies: 1
    Last Post: 10-04-2007, 08:23 PM
  5. Taco 003 Hot Water Circulator Pump Runs Hot!
    By gplumb in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 03-24-2007, 05:30 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •