    Unhappy Setting thermostat

    I want to set my AC thermostat to 73 and for it to come back on when the room reaches 75-76 degrees. Is this done using the offset or anticipator option and how would I set it for those options? Is the anticipator for heat only? Yeah I am so new to this.

  2. #2
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    The anticipator is for heat and is set to match the coil on your gas valve. It is not something you can adjust for your convenience.

    If you want closer swings, you will need a good programmable thermostat which has lots of user set-up features.

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default t'stat

    The differential is seldom adjustable because the greater the difference between the on/off temperatures, the longer the unit will have to run to satisfy the off setting. As a practical matter, the total run times will probably be the same. A small differential will just run for a shorter time more frequently. And in the process the humidity will increase adding to the AC load. The ideal system has the AC running fairly constantly to maintain an even temperature with maximum dehumidifaction, one reason for not using an oversized unit.