    Quote Originally Posted by Speedy Petey View Post
    Oh, I thought you were referring to copper.
    No, sorry, my mistake for not specifying. Either way, i agree with your feelings toward the 2008 changes.

  2. #17
    scratch-pad engineer and mechanical fabricator leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,314

    Default

    Quote Originally Posted by Billy_Bob View Post
    FYI - As to the label on the package and it saying "Ground Wire", the Andrew company sells large satellite and microwave dishes which require grounding. Thus I think they are "repackaging" this wire and calling it ground wire.
    Yes. I see, and that answers at least some questions I had. Thank you.

    Quote Originally Posted by Chris75 View Post
    Why dont you just go buy some 2/3 SER cable? good for 90 amps, or some 4/3 SER cable good for 65 amps. that wire is not that expensive.
    I do not know what SER cable is, but I will find out and take a look. There is a very reputable supply house nearby where I can get a contractor's price through my employer.

    I did some homework on the auction wire and I believe it might be okay (including the temperature rating) if the conduit is sized properly and I color-code the four strands, but I will not likely spend the time to first be absolutely certain about all of that unless cost becomes a really big issue.

    Thank you.

  3. #18
    Electrician Chris75's Avatar
    Join Date
    Aug 2007
    Location
    Litchfield, CT
    Posts
    608

    Default

    Quote Originally Posted by leejosepho View Post


    I do not know what SER cable is, but I will find out and take a look. There is a very reputable supply house nearby where I can get a contractor's price through my employer.
    This is SER type cable
    http://www.southwire.com/ProductCata...rodcatsheet273


    Quote Originally Posted by leejosepho View Post
    I did some homework on the auction wire and I believe it might be okay (including the temperature rating) if the conduit is sized properly and I color-code the four strands, but I will not likely spend the time to first be absolutely certain about all of that unless cost becomes a really big issue.

    Thank you.
    Unless that "free wire" is a Chapter 3 wiring method forget about it.
    Last edited by Chris75; 10-12-2008 at 05:33 PM.

  4. #19
    scratch-pad engineer and mechanical fabricator leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,314

    Default

    Quote Originally Posted by Chris75 View Post
    Unless that "free wire" is a Chapter 3 wiring method ...
    What "free wire", and Chapter 3 of what?

    Question: If I use the SER wire you mentioned, would I still have to run it in conduit?

  5. #20
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,226

    Default

    No but you would have to install a messenger wire to support the cable from being pulled on with added weight such as the wind or ice.

    EDITED TO ADD;

    Just though about something and wanted to be clear on the fact that SE-R cable can not be installed underground with or without conduit.
    338.12 Uses Not Permitted.
    (A) Service-Entrance Cable. Service-entrance cable (SE) shall not be used under the following conditions or in the following locations:
    (1) Where subject to physical damage unless protected in accordance with 230.50(A)
    (2) Underground with or without a raceway
    Last edited by jwelectric; 10-12-2008 at 07:19 PM.

  6. #21
    Like an engineer alternety's Avatar
    Join Date
    Apr 2006
    Location
    Washington
    Posts
    631

    Default

    I have read through this thread a couple of times and I am thinking things got off track part way through. In the fourth post, leejosepho describes the wire. It is a single stranded wire i.e., one #6 wire). It does not appear to be SER or multiconductor. It is copper. His garage is attached so it is not hanging over a span. It is rated THWN-2 which I think means it is ok for underground conduit (although there is no indication that the proposed use includes this) and use to 90*. It would think it ought to be in conduit because as he wants to use it it is simply 4 THWN single wires. Certainly for protection if it is exposed.

    Does this make sense?

  7. #22
    scratch-pad engineer and mechanical fabricator leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,314

    Default

    Yes, I probably confused things by asking about a second kind of wire in a thread originally asking about overhead service wire.

    My garage and workshop are attached to the house, so I need to run four wires to a panel that will not be bonded. My boss has a piece of twisted service wire I could use, but that would have to be in conduit and I would have to add an insulated neutral since the ground (service neutral) is already bare.

    To be more practical, the second piece of wire I have mentioned is #6 AWG, and it could be run as four strands in conduit as long as the ends are color-coded (black/black/white/green). But, maybe the SER wire Chris has mentioned can be run through walls without conduit?

  8. #23
    scratch-pad engineer and mechanical fabricator leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,314

    Default

    Quote Originally Posted by Chris75 View Post
    Why dont you just go buy some 2/3 SER cable? good for 90 amps ...
    You got me to thinking there, and I have decided to just go ahead and get whatever I need to replace my existing main (100-amp) panel with a 200-amp panel, and to then move the 100-amp panel to the workshop as a sub. I will let you know what wire the guys at the supply house recommend ...

    Thank you.