    Default Can overhead service wire be run inside conduit?

    I need to run 50' of wire to carry at least 60 amps (220) to the subpanel in my attached workshop, and the cost of the wire is presently keeping that project on hold. I can get a used length of twisted, 100-amp (outdoor overhead) service wire from a friend for virtually nothing, and I am asking if there is any problem with running that wire through conduit from my basement to the new workshop. I would have to add a 4th strand for the ground, and all of that might fit inside 1" conduit.

    Is there anything saying that particular service wire should not be run inside conduit and through walls?

    Thank you!

  2. #2
    In the Trades Bob NH's Avatar
    Join Date
    Oct 2005
    Location
    New Hampshire
    Posts
    3,308

    Default

    It's probably twisted and will be very hard to pull if there are any bends.

    You should untwist it, use a larger conduit (not more than 40% fill), and get some lubricant. You will also need to have some means to apply more tension than you can apply by yourself, and someone to push on the inlet end.

    Wire in conduit has a lower ampacity than is applied to overhead services applications.

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    23,534

    Default wire

    It is also probably aluminum with a bare neutral so you have to make provision for it when you connect it.
    Last edited by hj; 06-01-2008 at 10:29 AM.

  4. #4
    scratch-pad engineer and mechanical fabricator leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,314

    Default

    Quote Originally Posted by leejosepho View Post
    I need to run 50' of wire to carry at least 60 amps (220) to the subpanel in my attached workshop ...
    Can I use four strands of the wire in this picture?

    Here is the auction description:

    #6 AWG STRANDED INSULATED GROUND COPPER WIRE 250' ROLL

    Wire reads: REPUBLIC WIRE 6 AWG TYPE MTW OR THHN OR THWN-2 600V OR GASOLINE AND OIL RES II (UL) OR AWM-VW-1 SUN RES OR C-(UL) TYPE T90 NYLON OR TWN 75 E167613 FT1

    Thank you!
    Attached Images Attached Images  
    Last edited by leejosepho; 10-12-2008 at 04:14 AM.

  5. #5

    Default

    FYI - As to the label on the package and it saying "Ground Wire", the Andrew company sells large satellite and microwave dishes which require grounding. Thus I think they are "repackaging" this wire and calling it ground wire.

    Here is their info on this...
    http://awapps.commscope.com/catalog/...ls.aspx?id=361

  6. #6
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,226

    Default

    No to both questions

  7. #7
    Electrician Chris75's Avatar
    Join Date
    Aug 2007
    Location
    Litchfield, CT
    Posts
    608

    Default

    I agree with Mike, what your propose is a violation.

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    23,534

    Default garage

    As an aside, your garage will probably have a subpanel and that should be grounded with a ground rod, not necessarily a ground wire back to the original panel.

  9. #9
    Electrician Chris75's Avatar
    Join Date
    Aug 2007
    Location
    Litchfield, CT
    Posts
    608

    Default

    Quote Originally Posted by hj View Post
    As an aside, your garage will probably have a subpanel and that should be grounded with a ground rod, not necessarily a ground wire back to the original panel.
    ground rods are for lightning protection, not the ground your talking about. Oh, and attatched buildings with sub-panels do not require ground rods, but they do require 4 wires.
    Last edited by Chris75; 10-12-2008 at 06:32 AM.

  10. #10
    Electrician Chris75's Avatar
    Join Date
    Aug 2007
    Location
    Litchfield, CT
    Posts
    608

    Default

    Why dont you just go buy some 2/3 SER cable? good for 90 amps, or some 4/3 SER cable good for 65 amps. that wire is not that expensive.

  11. #11
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    922

    Default

    Quote Originally Posted by Chris75 View Post
    ...., or some 4/3 SER cable good for 65 amps. .
    MAN, the 2008 NEC SUCKS!

  12. #12
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    922

    Default

    Quote Originally Posted by chris75 View Post
    ground rods are for lightning protection, not the ground your talking about.
    +1 .............

  13. #13
    Electrician Chris75's Avatar
    Join Date
    Aug 2007
    Location
    Litchfield, CT
    Posts
    608

    Default

    Quote Originally Posted by Speedy Petey View Post
    MAN, the 2008 NEC SUCKS!
    Actually, # 4 would only be good for 55 amps under the 2008, glad we are not using it.

  14. #14
    Moderator and Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,003

    Default

    To be specific, that ground wire does not carry an insulation rating which would allow you to use it for "hot" conductors. It may be perfectly fine, but it is not rated...so don't use it.

  15. #15
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    922

    Default

    Quote Originally Posted by Chris75 View Post
    Actually, # 4 would only be good for 55 amps under the 2008, glad we are not using it.
    Oh, I thought you were referring to copper.