That does seem like a short cycle. Can't help in that regard, but wonder if the high/low settings are proper.
If a circulator isn't running while the burner is firing, the water in the heat exchanger could boil creating all sorts of problems.
An indirect WH is usually set up as a priority zone...i.e., it runs and shuts off all other heating zones temporarily until the WH has reached temp.