    Default Testing for gas leaks

    I am in the process of leak testing a gas line for a double wide modular home. The gas line is black iron pipe, and it only supplies two appliances, (a furnace, and the stove/oven combination). The home uses propane from a 250 gallon tank.
    I am using compressed air at 15 psi, with a gas pressure gage to test for leaks. At the 15 psi, I have found so far, a by-passing gas valve and a flex line connection leak. I have also found a leak where the black iron pipe screws into the regulator, (see photos) all at the furnace location. I have replace the valve, the flex line, and sealed up the leak at the pipe / regulator connection for the furnace area, (all tested again with soapy water).
    As I am getting closer to having the gas line, “bullet proof”, I also noticed that the stove/oven combination was leaking from an orifice on one of the burners. I have shut off the valve to the stove/ over.
    I have tested the main and branch lines to both of the shut off valves and they are bullet proof, and I still have a leak somewhere. I suspect that the air pressure is going through the regulator for the furnace. Could this be because the regulator is designed to operate at ˝ psi, and I have 15 psi supplied to it for the test? Could I have the same problem at the stove….too much supplied testing pressure? Could I have messed up the regulators for the furnace and the stove because of too high testing pressure?

    Thanks for the help on this one!

    Mike
    Attached Images Attached Images   

  2. #2
    Engineer Furd's Avatar
    Join Date
    Jul 2007
    Location
    Wet side of Washington State
    Posts
    446

    Default

    I hate to tell you but you quite likely destroyed that combination gas valve on the furnace.

    No combination gas valve that I am aware of will withstand an inlet pressure of 15psi. The valves are designated as having a MAXIMUM inlet pressure of 1/2 psi.

    It appears that you are using some salvaged fittings, that's a no-no. And why are you using a gate valve? Only approved AGA (American Gas Association) valves should be used in gas piping.

  3. #3
    Engineer Furd's Avatar
    Join Date
    Jul 2007
    Location
    Wet side of Washington State
    Posts
    446

    Default

    I'm sure I read "gate valve" in the description but now all I see is "gas valve".

    I have found AGA gas valves to be defective from the factory. One I found had a piece of fine steel wire embedded in the soft seat.

    In my area natural gas lines are usually tested to 3 psi for 4 hours. That is six times the maximum working pressure of 1/2 psi. There is no need to test such lines to 50 psi.

    A propane system usually has a primary regulator at the tank that is set at 10 psi and then a house regulator that is set at 11 inches of water column. Sometimes the house regulator is not used but a secondary regulator at each appliance is then used and set at 11 inches water column.

    When testing for long periods of time an allowance may need to be made for the temperature change from the time the test was applied to the end of the test period. If the temperature has dropped (typical for an overnight test) then the pressure in the line will also drop even with zero leakage.

  4. #4
    DIY Senior Member Mikebarone's Avatar
    Join Date
    Feb 2006
    Location
    Phoenix, AZ
    Posts
    206

    Default

    Quote Originally Posted by Furd View Post
    I hate to tell you but you quite likely destroyed that combination gas valve on the furnace.

    No combination gas valve that I am aware of will withstand an inlet pressure of 15psi. The valves are designated as having a MAXIMUM inlet pressure of 1/2 psi.

    It appears that you are using some salvaged fittings, that's a no-no. And why are you using a gate valve? Only approved AGA (American Gas Association) valves should be used in gas piping.
    Thanks so much for the info. That combination gas valve was on the furnace when I started working on the home, (with the sheet metal strap holding it on) nice. I did locate a 4-1/2" gas gage that has increments of 1/10 lb and a range of 0 to 15 lbs. for $27.50....probably a good investment huh.
    Do you know if there is a direct formula, to convert water column to air presure psi?

    Thanks again!

  5. #5
    Aspiring Old Fart, EE, computer & networking geek Mikey's Avatar
    Join Date
    Nov 2005
    Location
    Central Florida
    Posts
    2,686

    Default

    From another website:

    1" of water column = 0.0360 PSI and
    1 PSI = 27.7612 inches of water column

    Sounds right. If you remember that normal atmospheric pressure is about 14.7 psi, or 29.92" of mercury, and mercury is about 13.6 times as dense as water, the numbers all work out.

  6. #6
    DIY Senior Member Mikebarone's Avatar
    Join Date
    Feb 2006
    Location
    Phoenix, AZ
    Posts
    206

    Default

    Quote Originally Posted by Mikey View Post
    From another website:

    1" of water column = 0.0360 PSI and
    1 PSI = 27.7612 inches of water column

    Sounds right. If you remember that normal atmospheric pressure is about 14.7 psi, or 29.92" of mercury, and mercury is about 13.6 times as dense as water, the numbers all work out.
    Thank you very much for that info. I saved that one for later reference, for sure!

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default gas

    Here, and in many places, the gas lines are tested from the meter to the end of the CAPPED OFF flexible lines and the appliance line shutoff valves open. The test is at 10 psi, using a sensitive gauge with 1/10 increments. ANY drop is a leak and has to be located and repaired. You do not test to the regulators or appliance gas controls.

  8. #8
    DIY Senior Member Mikebarone's Avatar
    Join Date
    Feb 2006
    Location
    Phoenix, AZ
    Posts
    206

    Default Thanks so much!

    Quote Originally Posted by hj View Post
    Here, and in many places, the gas lines are tested from the meter to the end of the CAPPED OFF flexible lines and the appliance line shutoff valves open. The test is at 10 psi, using a sensitive gauge with 1/10 increments. ANY drop is a leak and has to be located and repaired. You do not test to the regulators or appliance gas controls.

    Thanks for the great advice. I hate to say it but live and learn. I took the range to a repair shop and I told them what I had done and I asked them if I might have messed up the ranges built in regulator, (by testing it at the 15 psi). He said, (be it fact or fiction…I hope fact) that if it was set up to run on LP gas, that I probably didn’t mess anything up because they operate at the 11 psi range, from the LP tank's regulator. Then I asked him if I might have messed up the control valve at the furnace, and he said almost the same thing. He said when the furnace is converted to run on LP gas, there is something, (didn’t get the name of it, because he was really busy) that is screw in to the control valve, and by screwing it in, it will disengage the built in regulator. Now he did say that if both of them were set to run on natural gas I would have damaged them for sure, because the pressure is down around ˝ psi.
    I left the stove with him to check out anyways because I did get more of a, “leak indication” from testing the main line, and then, when I opened the valve to the range and tested again. Then again…it could be something I messed up. I hate learning the hard way, but boy it sure sticks with you when you do.

    Thanks so much,

    Mike

  9. #9
    Plumber Winslow's Avatar
    Join Date
    Dec 2005
    Location
    Hawaii
    Posts
    450

    Default

    Quote Originally Posted by hj View Post
    Here, and in many places, the gas lines are tested from the meter to the end of the CAPPED OFF flexible lines and the appliance line shutoff valves open. The test is at 10 psi, using a sensitive gauge with 1/10 increments. ANY drop is a leak and has to be located and repaired. You do not test to the regulators or appliance gas controls.

    Here in hawaii I test the rough piping (up to the appliance) with 6" mercury. Then when I set fixtures I hook everyhting up, turn on the valve at the appliance (the appliance itself is off) and test a either 12" or 14" water column, depending on if the system is nat or lpg. The gas company here will not hook up the tank unless they see the valves to the fixtures open and it holds the water column without dropping for 15 minutes..

    I used to pressure test with air but it takes too long to determine if it has a leak. A manometer will tell you immediately if you have a leak.

  10. #10
    DIY Senior Member Mikebarone's Avatar
    Join Date
    Feb 2006
    Location
    Phoenix, AZ
    Posts
    206

    Default

    Quote Originally Posted by winslow View Post
    Here in hawaii I test the rough piping (up to the appliance) with 6" mercury. Then when I set fixtures I hook everyhting up, turn on the valve at the appliance (the appliance itself is off) and test a either 12" or 14" water column, depending on if the system is nat or lpg. The gas company here will not hook up the tank unless they see the valves to the fixtures open and it holds the water column without dropping for 15 minutes..

    I used to pressure test with air but it takes too long to determine if it has a leak. A manometer will tell you immediately if you have a leak.
    I have used, (about 25 years ago) a mercy tester. At the risk of exposing my ignorance, what does the term, “Water column” refer to? Is there a water column testing device as there is a mercy testing device? I’ve tried to look it up on the net, but so far I haven’t had any luck finding a, “water column tester”. I did find a manometer on the net. I’ve called around to the local rental companies, and I guess they don’t rent mercy testers any more, (probably because of the mercy liability itself). Thanks so much for all of the wealth of information; it is greatly appreciated!

    Mike

  11. #11
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default test

    Mercury gauges were the standard here, until mercury became a nasty word. Then the 10 psi air test became the standard. The LP person was wrong. The appliance regulators are set for 11 INCHES, not pounds. The tank regulator is high pressure but that has nothing to do with the line you are testing. Fortunately, in many cases the appliance regulators will "lock out" and not be damaged, but there is no assurance that they will not be damaged by excessive pressure.

  12. #12
    DIY Senior Member Mikebarone's Avatar
    Join Date
    Feb 2006
    Location
    Phoenix, AZ
    Posts
    206

    Default

    Quote Originally Posted by hj View Post
    Mercury gauges were the standard here, until mercury became a nasty word. Then the 10 psi air test became the standard. The LP person was wrong. The appliance regulators are set for 11 INCHES, not pounds. The tank regulator is high pressure but that has nothing to do with the line you are testing. Fortunately, in many cases the appliance regulators will "lock out" and not be damaged, but there is no assurance that they will not be damaged by excessive pressure.

    Based on your response, (that I thank you for very much) I think I might have messed up the control valve on the furnace, (photo above). I think it is by-passing in the off position, but I’m going to wait to test it until I get a manometer. That repair guy told me those control valves range from $100.00 to $500.00 so if I don’t learn from this one, something is wrong.
    So is there a, “water column testing device, or is the phrase, “water column” just a term that is used, and that everyone just converts it to, “pounds per square inch”?

    Thanks again,

    Mike

  13. #13
    Aspiring Old Fart, EE, computer & networking geek Mikey's Avatar
    Join Date
    Nov 2005
    Location
    Central Florida
    Posts
    2,686

    Default

    You can make a "water column testing device", aka manometer, by bending a piece of flexible plastic tubing into a U shape. If you're going to be looking for around 11" of water, make the legs of the U about 20" long. Fill the U about half-full of water, so there's about 10" of water in each leg. Now connect the system to be tested to one end of the U and leave the other end open. As the system is pressurized, the water will be forced down in the connected leg, and will rise in the open leg. When the difference in height is 11", you've got 11" of water in the pressurized system. If there's a leak in the system, the pressure will eventually fall to 0", when the heights in the two legs of the U are equal.

    There's an interesting application of a homemade water manometer, with detailed instructions for its construction, at http://www.bagpipejourney.com/articles/manometer.shtml.

    Or, you're not experimentally inclined, you can buy a commercially available water manometer for $20 (and up):
    http://store.noahsarkhomecare.com/fipawacoma.html

    Google "water manometer" for a wide selection available on line.

  14. #14
    DIY Senior Member Mikebarone's Avatar
    Join Date
    Feb 2006
    Location
    Phoenix, AZ
    Posts
    206

    Default

    Quote Originally Posted by Mikey View Post
    You can make a "water column testing device", aka manometer, by bending a piece of flexible plastic tubing into a U shape. If you're going to be looking for around 11" of water, make the legs of the U about 20" long. Fill the U about half-full of water, so there's about 10" of water in each leg. Now connect the system to be tested to one end of the U and leave the other end open. As the system is pressurized, the water will be forced down in the connected leg, and will rise in the open leg. When the difference in height is 11", you've got 11" of water in the pressurized system. If there's a leak in the system, the pressure will eventually fall to 0", when the heights in the two legs of the U are equal.

    There's an interesting application of a homemade water manometer, with detailed instructions for its construction, at http://www.bagpipejourney.com/articles/manometer.shtml.

    Or, you're not experimentally inclined, you can buy a commercially available water manometer for $20 (and up):
    http://store.noahsarkhomecare.com/fipawacoma.html

    Google "water manometer" for a wide selection available on line.
    Thank you, thank you, thank you, you have cleared up, (one of the many) fogged up things in my mind. I will check out those web sites, and I'll get one or try to build a water column tester. And maybe, just maybe, I won’t mess up any more control valve!

    Thank you again!

    Mike

  15. #15
    DIY Member Squ1rrel's Avatar
    Join Date
    Dec 2007
    Location
    Texas
    Posts
    69

    Default

    Digital Manometers read the same thing, only without the actual water, and are generally more accurate.
    http://www.ueitest.com/product-em150.html
    this is the one our in-house techs use to test gas valves.