    I am in the process of remodeling my daughter's condo and have to move some electric. It has a fire rated ceiling (two levels or tiers) and the wiring was run through the ceiling room to room.

    Is it permissable (to keep from tearing into the ceiling) to re-route some wiring through the wall(s) framing? Can the replaced/dead circuits that will pass through the ceiling be cut off and left before dry walling?

    This is in MD.

    Your help is appreciated.

    Gary
    Jack of All Trades...

    ...Master of None...

  2. #2

    Default

    Get a book on electrical wiring and you will see that a lot of wiring is run in walls. Especially one outlet, to the next outlet, to the next, etc.

    This is to save cost on wire. Shortest distance is a straight line.

    But when running wires through walls, there are a lot of studs to drill holes through. So If I am running a wire from one room through the next room and on to another room further away, I'll run it in the ceiling or attic. Then I don't need to drill a bunch of holes.

    Also drilling too many holes or very large holes in studs will weaken them. Might want to get a construction code check book when covers all codes including plumbing. Then this will tell you how large of a hole you can have in each stud depending on if it is a bearing wall or not. (Look in plumbing section.)

    As to leaving dead wires in walls/ceilings, as a general rule I don't do this if I can remove the old wire. Then there is not a bunch of old wires running all over the place making it difficult to trace circuits. (Hummm... Where does this wire go to?) I don't know if there are any code rules on this?

  3. #3
    Jack of all trades, Master of none KULTULZ's Avatar
    Join Date
    Nov 2006
    Location
    ROCKVILLE, MD
    Posts
    85

    Post

    Thanx for the reply.

    The main problem is the wiring running through the top plates have had a mastic applied to them to prevent smoke infiltration in case of a fire. The drywall is 5/8" fire rated and is very heavy so making exploratory holes would be a pain to patch. I was thinking of just cutting the wires at the top plate and rerun through the wall studs (non-load bearing).

    The lower ceiling is so close to the first that recessed lighting cannot be used.
    Jack of All Trades...

    ...Master of None...

  4. #4
    Aspiring Old Fart, EE, computer & networking geek Mikey's Avatar
    Join Date
    Nov 2005
    Location
    Central Florida
    Posts
    2,686

    Default

    Quote Originally Posted by KULTULZ View Post
    I was thinking of just cutting the wires at the top plate and rerun through the wall studs (non-load bearing).
    That will work. Be sure to cut both ends of the cables at the top plate, and be sure they're not live -- although they won't be live for long . When going through a stud, the edge of the hole must be at least 1 1/4" from either edge of the stud. This means that for a 3 1/2" stud, you must drill the hole in the center of the stud, and the hole can be a maximum of 1" in diameter, as far as the NEC is concerned. Other construction codes may limit the size of the hole further. You can also just cut a groove in the stud and place the cable(s) in the groove, but they must be protected by a 1/16" steel plate.

    See 300.4 in the Code for the gory details.

  5. #5
    Jack of all trades, Master of none KULTULZ's Avatar
    Join Date
    Nov 2006
    Location
    ROCKVILLE, MD
    Posts
    85

    Post

    Quote Originally Posted by Mikey View Post

    That will work. Be sure to cut both ends of the cables at the top plate, and be sure they're not live -- although they won't be live for long . When going through a stud, the edge of the hole must be at least 1 1/4" from either edge of the stud. This means that for a 3 1/2" stud, you must drill the hole in the center of the stud, and the hole can be a maximum of 1" in diameter, as far as the NEC is concerned. Other construction codes may limit the size of the hole further. You can also just cut a groove in the stud and place the cable(s) in the groove, but they must be protected by a 1/16" steel plate.

    See 300.4 in the Code for the gory details.
    Thank You!

    I was hoping someone would say that...