Just bought a house that had been "winterized" for about 8 months. After de-winterizing all was well EXCEPT I get ZERO hot water flow from one of the Delta pressure-balancing tub/shower valves. It's about 15 or so years old. Any advice on where to star looking for the problem??
 

Krow

Plumber
Messages
903
Reaction score
3
Points
16
Location
Ontario, Canada
Your balancing spool may be stuck. It shood be located behind the face plate of the faucet. It looks like a 1" diameter slotted screw.
 

jasdyer

New Member
Messages
3
Reaction score
0
Points
0
Thanks Crow

Let's say I find it and assume that it's stuck. Now what? Hammer, screwdriver, wd-40? How do I unstick it?
 

Krow

Plumber
Messages
903
Reaction score
3
Points
16
Location
Ontario, Canada
1)You can try tapping on the large screw (Sometimes it will unstick).

2)You can shut off your water and try to unscrew that large screw. Once its out
------a) Try tapping the entire spool on something hard and see if it loosens
------- b ) purchase an identical balancing spool and replace it
---------------- i) maybe HD
-------------- ii) plumbing supply house
---------------iii) call delta for replacement part
 

jasdyer

New Member
Messages
3
Reaction score
0
Points
0
Thanks, again, Krow!

Will do! I was kidding about the hammer! Guess I might use it after all. I appreciate the tips.
 