Results 1 to 9 of 9
Thread: Outdoor spa wiring questions
    DIY Junior Member MJ32V's Avatar
    Feb 2008
    NY
    Default Outdoor spa wiring questions
    Is it a problem (code or otherwise) to locate outdoor hot tub over a 7' run of buried rigid sched 40 PVC conduit? Conduit is buried in 20" of item #4 with unilock paver on top side. Tub is 450 gallon.
    Another question... what are min/max distance requirements - from the tub to outlet - for locating 20A GFCI outlet?
    Thx...
    MJ
    Jun 2007
    North Carolina
    Quote Originally Posted by MJ32V View Post
    Yes
    Thx...
    MJ
    No closer than 10 feet and no more than 20 feet
    I do not see any problem with placing a portable hot tub over a conduit buried over 18 " underground. That is why you bury it.
    Jun 2007
    North Carolina
    Quote Originally Posted by ked View Post
    See Article 680 of the NEC
    Feb 2008
    NY
    I was told that there is an exception in 680.10 that allows buried conduit underneath spa as long as that conduit supplies power to spa. Can someone confirm for me?
    With respect to GFI duplex, does the 10' min / 20' max distance requirement also specify duplex be line of sight from tub?
    Jun 2007
    North Carolina
    Not under the tub but it is allowed closer that 5feet if it supplies the tub.
    No
    Feb 2008
    NY
    Hmmm... I see that interpretations may vary on this. Here's 680.10:
    680.10 Underground Wiring Location. Underground wiring shall not be permitted under the pool or within the area extending 1.5m (5 ft) horizontally from the inside wall of pool unless this wiring is necessary to supply pool equipment permitted by this article. Where space limitations prevent wiring from being routed a distance 1.5 m (5 ft) or more from the pool, such wiring shall be permitted where installed in complete raceway systems of rigid metal conduit, intermediate metal conduit, or a nonmetallic raceway system. All metal conduit shall be corrosion resistant and suitable for the location. The minimum cover depth shall be as given in Table 680.10.
    Based on the wording, it seems that wiring buried in conduit would be allowed underneath the tub as long as it was the tub's supply. Anyone else want to weigh in on this?
    MJ
    Central Florida
    Whatever made you think there was a conduit under the spa?
    Jun 2007
    North Carolina
    MJ
    What is preventing the branch circuit supplying from being around the perimeter instead of under?
    One would be hard pressed to explain away those words in bold above.
    To just say that running the conductors under the tub is easier would not be a reason to install then around the tub.
    On the other hand it would be better to have the supply panel on the same side the conductors are coming from.