    Hello - Could someone please look at the attached image and let me know what you think (its my first attempt at this). Any advice, giudes etc are warmly received.

    Room Dimensions - 9'ish x 5'ish

    Main stack to red vertical vent pipe = 59"
    Main Stack to Proposed wc pipe = 48"

    I'm trying to achieve:

    Basement A - plumb wc, vanity sink and tub into the basement. I have added the wye in the image to the 4" main horizontal stack. is this the right size 4" and placement?

    Third Floor B - Secondly I need to include a 3" ABS vertical pipe to the third floor in preperation for the new bathroom in the future (inc tub, vanity sink & toilet) is this the right size pipe placement and linkage?

    (NOTE) the tub pipe/location is not shown - however, the the location would run parallel to the right wall as you look at the image.

    Finally - how would I tie in the orange and yellow pipe to the main blue pipe + I was told you can only use PVC below grade and everything else aobve grade is ABS - though some people say you should stick with the same material (Canada)?

    I hope that makes sense I will re post new image with inclusions of any cool advice given.

    thank you for your time and professionaisn in this matter

    novicepiper

    PS i forgot to mention I was thinking of increasing the vertical orange pipe tp 2" to accomodate the venting of the kitchen sink and the basement vanity sink - could i do that/ would that work?
    Attached Images Attached Images  
    Last edited by novicepiper; 04-30-2008 at 08:10 PM. Reason: omission

  2. #2
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Nice drawing.

    Not clear about the orange pipe. Is it a waste pipe from the kitchen? . The big question is, how are you venting the basement fixtires?

    Unless Canada has different rules, ABS and PVC can both be used below grade down here, and you should not try to mix material.

    Helpful Plumbing Hints for Residential Construction by Bert Polk Plumbing Inspector Lincoln County
    Last edited by Terry; 05-24-2010 at 03:33 PM.

  3. #3
    Not a Master Plumber novicepiper's Avatar
    Join Date
    Apr 2008
    Location
    CAN Toronto GTA
    Posts
    97

    Default Reply to Jimbo 1

    Hi Jimbo Thanks for looking at this for me - please find attached NEW image showing the tub placement with added explanation for orange pipe and basement fixture venting.
    the orange pipe was originally tied into the blue pipe.....i have not touched the plumbing as yet - this is more of a plan and info exercise to help me understand a little more abuot venting etc


    ps if anyone else would be kind enough to look at this, that would be awesome

    thanks

    novice plumber

    & i will be posting a couple more images re tub placement in around ten mins from now.
    Attached Images Attached Images  
    Last edited by novicepiper; 05-01-2008 at 07:39 AM.

  4. #4
    Not a Master Plumber novicepiper's Avatar
    Join Date
    Apr 2008
    Location
    CAN Toronto GTA
    Posts
    97

    Default close up of tub pipe, main stack and proposed 3" 3rd floor pipe

    im not too sure on the linkage of the green pipe to the blue - I used 4x4x3 wye 45 and 90 elbow (cant seem to find a sweep).... could i just use a 45 from the vertical green pipe and run it straight into the 4x4x3 wye? (this exceeds the pitch of 1/4 per ft or 1/8 per ft)?

    still not too sure on how to link the yellow and orange pipe to the blue pipe

    thanks for any advice given - greatly appreciated
    Attached Images Attached Images  
    Last edited by novicepiper; 05-01-2008 at 07:36 AM. Reason: pitch

  5. #5
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    I moved this threas up to the plumbing section so we could see all your diagrams in one spot. It confuses the issue when you get multiple threads going on the same subject.

    Jim

  6. #6
    Not a Master Plumber novicepiper's Avatar
    Join Date
    Apr 2008
    Location
    CAN Toronto GTA
    Posts
    97

    Default

    Quote Originally Posted by jimbo View Post
    I moved this threas up to the plumbing section so we could see all your diagrams in one spot. It confuses the issue when you get multiple threads going on the same subject.

    Jim
    Thanks Jim - im not too sure how to sort threads out as yet - i would have just deleted this since the new configuration has slightly changed - thanks again

    novicepiper

  7. #7

    Default Nice Drawing

    What program did you use the draw the pipeing....
    I am working on a similar problem and need to work on my drawings.

  8. #8
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    In his other thread he posted this info about the software he used...

    SOFTWARE TITLE: 3ds max
    COMPANY: Autodesk
    Price: 3K+ tax depends on what version you buy.

    You can download a free trial but if you've not done any 3d before, it prob going to be more work than results

  9. #9
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default Dwv

    1. The toilet is not vented, and the third floor bathroom will create a big problem for it until it is vented.
    2. The overflow for the tub does not connect to the trap's vent.
    3. The intermediate vent on the line to the lavatory is doing nothing and is not needed.
    4. There are many ways to make the final connections. Which one is "best" will be determined by exactly how much space you have to do it.

  10. #10
    In the Trades
    Join Date
    Feb 2009
    Location
    North East PA / New Jersey
    Posts
    3

    Default

    Hi, I wish I would have found this site some time ago. I just installed my DWV system in my home and think I went over board with vents :-)! If I may ask, where can I get this drawing software that is used in this thread. I sure can use it for my water system that I will be installing shortly.
    Please foregive me for the re-direction and thanks again for your time.
    Joe

  11. #11
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Don't say you went overboard with vents. This thread, which died out without apparent final feedback....he never did show us ANY vents for the basement bathroom.....BAD!

  12. #12
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    Actually the other thread I believe ended up being shown with all the vents.
    I believe post #8 above shows the software he used.

  13. #13
    Not a Master Plumber novicepiper's Avatar
    Join Date
    Apr 2008
    Location
    CAN Toronto GTA
    Posts
    97

    Default

    Quote Originally Posted by Redwood View Post
    Actually the other thread I believe ended up being shown with all the vents.
    I believe post #8 above shows the software he used.
    Software was 3dsmax and I honestly thought after all the excellent advice on here I received re bathroom layout; bathroom venting and entire Drains, waste and venting were correct as redwood mentioned regarding other thread posting.

    Well before I finshed all the work: I had Pro come over and look at it, some small mods. He said what I had done would work famously and I have had no issues at all with any floor in the house....no smells everthing works well strong flushes no blockages....only 2 minor things still persist.

    I can`t seem to figure out the ball cock in the back of the basement toilet..I always seem to overflow the toilet (probably 1 inch of extra water in the toilet)via cistern when refilling. I`ve tried adjusting the vertival nut and extending.retracting the arm but what ever i do after a few days it just goes back to overflowing a little or not enough water fills...that`s just plain weird I thought...!?

    the other issue is a smal gurgle when the second floor toilet flushes - seems to happen mid empty flush - I dont have any leaks and all the venting was appoved by this pro guy (which is also a friend) anyways that aside as long as the gurgle is not an issue evrything is champion...

    ps any ideas what could be causing ther gurgle (i yhough it may be an air leak on the seal of the toilet or something)(ocassionally i get a little water around the base)in the second floor toilet mid flush?

    thank all as always

    novice piper
    Last edited by novicepiper; 03-19-2009 at 04:25 PM.

  14. #14
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    Sounds like a bad fill valve... Replace it with a Fluidmaster 400A.
    And your other problem sounds like a bad seal on the wax ring.

  15. #15
    Not a Master Plumber novicepiper's Avatar
    Join Date
    Apr 2008
    Location
    CAN Toronto GTA
    Posts
    97

    Default

    Quote Originally Posted by Redwood View Post
    Sounds like a bad fill valve... Replace it with a Fluidmaster 400A.
    And your other problem sounds like a bad seal on the wax ring.
    thanks and thanks

    Ill replace both over next couple of days. athnks again for all your continued support through this reno - nice to know there still decent people about