    I recently replaced an electric water heater with a new one.
    The old water heater had 4500 watt elements on a two pole 30 amp breaker
    The new water heater has 5500 watt elements. the problem is periodically the breaker in the panel is tripping. Acording to the water heater specs the amperage should only be 22.9. Is it a problem if I replace the 30 amp breaker with a 40 amp breaker. I would run new # 8 wire to the water heater or should i just replace the existing 30 amp breaker with a new one.

  2. #2
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Something is wrong somewhere. Upgrading the circuit will likely fix this but it will only mask the real problem.
    A 30A breaker is fine for a 5500w water heater, and should NOT be tripping on that load.

    Replacing the 30A breaker would be an easy and cheap place to start.

  3. #3

    Default Electrical Wire

    I replaced the 30 amp breaker with a new one. I'll see what happens.
    It appears the wire is #12 wire. Could this cause the breaker to trip

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default wire

    It should be #10 for 30 amps. It is probably overheating, but it should not trip the breaker. If anything it should start a fire.

  5. #5
    Electrician frenchelectrican's Avatar
    Join Date
    Jun 2007
    Location
    NE Wis / Paris France { In France now }
    Posts
    46

    Default

    Quote Originally Posted by marinelli44 View Post
    I replaced the 30 amp breaker with a new one. I'll see what happens.
    It appears the wire is #12 wire. Could this cause the breaker to trip

    now that is the issue with #12 wire with 30 amp breaker and with 5500 watts running thru it and 5500watts @ 240 volts = 22.9 amps IMO it pretty light with this wire size it will be wiser to bump up to #10 wire and while you are at it if your water heater is not in the sight of breaker box [ if the water heater is in diffrent room or divided then you have a disconnect switch next to the waterheater.

    Merci,Marc

  6. #6
    Plumber Cass's Avatar
    Join Date
    Nov 2005
    Location
    Ohio
    Posts
    5,984

    Default

    DO NOT USE a 30A breaker on the #12 wire unless you want to remodel your house due to a fire.

    You may also be attending the funeral of a loved one if you do.

  7. #7

    Default Water heater

    I replaced the #12 wire with #10. The breaker is still tripping periodically. Being this is a new water tank I'm calling the manufacturer.

  8. #8
    Computer Programmer Bill Arden's Avatar
    Join Date
    Sep 2006
    Location
    MN, USA
    Posts
    584

    Default

    It sounds like the upper temperature switch is bad and is turning on both elements at the same time.

    Either that or something is shorting out.
    Important note Ė I donít know man made laws, just laws of physics
    Disclaimer: I'm a big fan of Darwin awards.