The service conductors are required to terminate outside or inside nearest the point of entry.
This means that they can not be routed around in the walls or any other place except where they come through the wall.
Remember that the service conductors do not have overcurrent protection so to run them on the inside of the wall would mean that there would nothing to blow or open in the event something went wrong.