This Grey Box, is an Intermatic timer for my water heater. I have off-peak metering, but this timer is not wired properly.

Can someone please tell me the proper wiring for this unit? I've called Intermatic but they were not very helpful as I was on hold for a very long time waiting for a tech. There is 10-3 coming into the box.

Thanks,
Molo
 

Attachments

  • grey100_1419.jpg
    grey100_1419.jpg
    36.3 KB · Views: 1,340
  • inside100_1421.jpg
    inside100_1421.jpg
    39.2 KB · Views: 2,227
  • wires100_1425.jpg
    wires100_1425.jpg
    34.4 KB · Views: 1,178

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
Terminals 1 & 3 are the LINE side,(from the panel) 2 & 4 are the LOAD side, they go to the heater... not sure why they ran 10-3, but your not going to be using one of the conductors...
 

Molo

Member
Messages
922
Reaction score
2
Points
18
Location
Cold New York
Better Pictures

Some Better Pics,

I believe this is a wiring problem, I have set these timers succesfully in the past, and this one continues to come on based on demand, not the timer. I have to use the manual lever if I want it to turn off.

Thanks for looking,
Molo
 

Attachments

  • wiring100_1428.jpg
    wiring100_1428.jpg
    49.6 KB · Views: 1,369
  • cover100_1430.jpg
    cover100_1430.jpg
    42.1 KB · Views: 1,168

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
How is the water heater wired? Is the blue and yellow tied together at the heater? Its obviously wired wrong... just not sure why they ran 3 conductors to the water heater.
 

Molo

Member
Messages
922
Reaction score
2
Points
18
Location
Cold New York
better pic. of inside of timer

A slightly better pic of the inside of the timer. The water heater doesn't pay attention to the timer. It turns on when there is demand. I've set these timers before with no problem, this is why I believe it may be a wiring problem.

Thanks for looking,
Molo
 

Attachments

  • betterpic100_1427.jpg
    betterpic100_1427.jpg
    50.1 KB · Views: 1,447

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
I have no idea what that blue is, but both yellows (I assume the load 240v) are on the same terminals as the red and black feed. The switch is doing nothing.
 

Molo

Member
Messages
922
Reaction score
2
Points
18
Location
Cold New York
As you can see in the first pic. The timer is supplyed by 10-3. The timer then supplys the water heater through the flexible metal conduit.

The white from the 10-3 is in a wire nut all alone. The Large blue from the armored conduit does not go in the wire nut with the white from the 10-3. (the picture is deceiving)

Thanks for any input,
Molo
 

Molo

Member
Messages
922
Reaction score
2
Points
18
Location
Cold New York
Pics of Upper & Lower Element Wiring

Pics of Upper & Lower Element Wiring. This is the best way of showing what the blue does.

Thanks again,
 

Attachments

  • upper100_1432.jpg
    upper100_1432.jpg
    37.2 KB · Views: 1,120
  • lower100_1433.jpg
    lower100_1433.jpg
    33.2 KB · Views: 1,170

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
The two hot leads from the power panel need to go to terminals 1 and 3 (doesn't matter which one goes where). Then, the two leads that go to the WH need to go on terminals 2 and 4. You have no connection on terminal 4. It MIGHT work, since it appears you have one lead connected to the hot line input, but won't work via the automatic switch. What you have is one hot lead connected to the WH all the time; the switch is only switching one lead, not opening both.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
http://www.intermatic.com/images/instruction_sheets/wh40.pdf

http://waterheating.rheem.com/content/resources/documents/use_care/ResElecProfessional.pdf

You will need the wiring diagram for your water heater. The second link above is for Rheem, and may be instructional. Figure F on page 20 of the manual is how yours likely would be wired. It appears that in this configuration, the upper element is always live, but the lower element is controlled by the timer.

Can't tell from the pics of your water heater how that switched wire is connected, but it appears your t-stat configuration may not be compatible with timer operation. In any event, find the wiring instructions for your model, and go from there.
 

PEW

DIY Senior Member
Messages
484
Reaction score
0
Points
16
If you have off peak metering, that should be controlled by the off peak meter outside your house, which is under the control of the electric company, not a timer which you can control.
 

Molo

Member
Messages
922
Reaction score
2
Points
18
Location
Cold New York
http://www.intermatic.com/images/instruction_sheets/wh40.pdf

http://waterheating.rheem.com/content/resources/documents/use_care/ResElecProfessional.pdf

You will need the wiring diagram for your water heater. The second link above is for Rheem, and may be instructional. Figure F on page 20 of the manual is how yours likely would be wired. It appears that in this configuration, the upper element is always live, but the lower element is controlled by the timer.

Can't tell from the pics of your water heater how that switched wire is connected, but it appears your t-stat configuration may not be compatible with timer operation. In any event, find the wiring instructions for your model, and go from there.


Thanks Jimbo,
You may be right that only the lower thermostate can be controlled by the timer. There was a handwritten note on the upper thermostat cover to that effect. I'll have to look closer at the diagram and the wiring.
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
You may be right that only the lower thermostate can be controlled by the timer. There was a handwritten note on the upper thermostat cover to that effect.
Well that would have been convenient information to have from the beginning. :rolleyes:
 

Molo

Member
Messages
922
Reaction score
2
Points
18
Location
Cold New York
Sorry Speedey, I didn't want to confuse the issue. I thought that showing the actual pics would be better than a note that was written a long time ago, and figured wiring could have changed since then.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
wiring

That is the way the timer is wired, but until you gave us that information, and the second set of pictures so we could see that it was the reason for the blue wire, we could not figure out why it was that way. Normally the timer controls the entire heater and it is not operated during the daytime. Therfore, all usage is off peak. The downside is that if the heater does not have enough capacity to take care of the hot water needs during the day, eventually you will be using cold water until the timer activates the heater.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
As far as the so-called off peak, etc. I think there are two different situations.
1) The electric company simply has a meter that records TIME as well as usage. KW's used during off-peak hours are billed at a lower rate. I surmise this is the situation with the current poster. The timer is installed so that during the peak hours, the lower element would never come on, but if a lot of water was used, the upper would eventually come on.

2) The electric company actually controls your unit....with the ability to shut you off if their circuits are nearing brownout condition. I have only seen this done with air conditioning, but seems like WH would also be an appropriate application of this technique.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks