Thread: Lining a well casing

  1. #1
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,150

    Default Lining a well casing

    My home's well has a 6 inch galvanized casing that is about 50 years old. We have some issues with rust coming out of the well. I was thinking that in the future when the submersible pump is replaced it might be a good idea to install a new PVC casing inside the existing galvanized casing.

    I'm wondering if this is something that is ever done or if anyone sees any problems with the idea? The one issue I see is that the pitless adapter will need to be dug up and fitted in the new casing. On the other hand it will probably be time for a new lateral (if we are going to do it right anyways).

  2. #2
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    You would probably only be able to get 3" PVC in that 6" casing. This greatly limits your choices of pumps. The worst thing is that you will still have the rust. Now the rust is between the two pipes and you canít clean it out. I would either clean out the galv casing with something like Cotey Chemicals, a well brush, and bailer, or drill a new well for 5" PVC.

  3. #3
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    And your casing my be only into the bedrock and the rest of the well is a hole in the rock or...

    The "rust" in your water may be dissolved ferrous iron and not from the casing anyway.

    Most casing is black iron pipe that can be rusted before it is used and I've never seen any galvanized well casing and now PVC is used too.

    So get a water test for hardness, iron, pH and tell us if the water is ever visibly dirty etc. and describe your water quality problems. Then we can help you decide what the actual cause of your problem is.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  4. #4
    Previous member
    Join Date
    Jul 2005
    Location
    Riverview, Fl.
    Posts
    4,540

    Default

    I would think you could get 4" PVC in that six inch hole if it's not all crusted inside. There should be room for 4" and it's couplings. Or go with 160 psi PVC with belled ends. I would use a rubber boot or a K-Packer on the bottom just to seal it off as well as possible.

    bob...

  5. #5
    DIY Junior Member tomjv's Avatar
    Join Date
    Dec 2012
    Location
    Somers, ny
    Posts
    3

    Default line your well

    Sorry to be responding so late on this but who knows, it may still help you or someone else.

    MY PROBLEM: (if anyone cares! haha)
    As it turns out, I have a different problem which requires a similar solution. I THINK I'm getting ground water into my well. My chloride levels are high enough to taste and I'm getting very cloudy water, especially after a soaking rain. We've been filtering our drinking water with R.O. and the whole house with a 20gpm particulate filter. Rather than drill a new well, I've been wanting to repair this one. First, I wanted to see what was going on down there. I ran the water to bring the head down, then lowered a camera/flashlight on a string. I used one of those helmet cams. I was able to get a great video of the inside. It looks like mine's leaking groundwater where the casing meets the bedrock. Anyway, that's MY issue. We both need our wells lined to fix them.

    TWO SOLUTIONS: (according to my well guy with 40+ yrs experience)
    1. Sleeve the well with 6" O.D. PVC. This is a "one way trip" as the PVC can never be removed. It must be done with a derrick. The PVC is pressed into the casing.
    2. Insert a smaller Diameter PVC. I don't remember the size, but my well guy says it's plenty to allow for a pump. There's a rubber gasket between the PVC and the casing which seals out bad stuff. The way I see it is, even if it seals out 70 or 80%, it's WAY better than it was. depending on your problem, this may provide part of a two step fix, i.e. installing some filtration inside etc.

    I haven't done anything yet, but will post when I do.
    TomJV
    ..................

    My home's well has a 6 inch galvanized casing that is about 50 years old. We have some issues with rust coming out of the well. I was thinking that in the future when the submersible pump is replaced it might be a good idea to install a new PVC casing inside the existing galvanized casing.

    I'm wondering if this is something that is ever done or if anyone sees any problems with the idea? The one issue I see is that the pitless adapter will need to be dug up and fitted in the new casing. On the other hand it will probably be time for a new lateral (if we are going to do it right anyways).[/QUOTE]

  6. #6
    DIY Junior Member tomjv's Avatar
    Join Date
    Dec 2012
    Location
    Somers, ny
    Posts
    3

    Default

    Here's a good article on the subject!



    My home's well has a 6 inch galvanized casing that is about 50 years old. We have some issues with rust coming out of the well. I was thinking that in the future when the submersible pump is replaced it might be a good idea to install a new PVC casing inside the existing galvanized casing.

    I'm wondering if this is something that is ever done or if anyone sees any problems with the idea? The one issue I see is that the pitless adapter will need to be dug up and fitted in the new casing. On the other hand it will probably be time for a new lateral (if we are going to do it right anyways).[/QUOTE]

  7. #7
    DIY Junior Member tomjv's Avatar
    Join Date
    Dec 2012
    Location
    Somers, ny
    Posts
    3

    Default

    Oops, I'm too quick on the keyboard!
    http://des.nh.gov/organization/commi...s/dwgb-1-9.pdf
    TomJV



    My home's well has a 6 inch galvanized casing that is about 50 years old. We have some issues with rust coming out of the well. I was thinking that in the future when the submersible pump is replaced it might be a good idea to install a new PVC casing inside the existing galvanized casing.

    I'm wondering if this is something that is ever done or if anyone sees any problems with the idea? The one issue I see is that the pitless adapter will need to be dug up and fitted in the new casing. On the other hand it will probably be time for a new lateral (if we are going to do it right anyways).[/QUOTE][/QUOTE]

  8. #8
    DIY Senior Member craigpump's Avatar
    Join Date
    Apr 2012
    Location
    ct
    Posts
    713

    Default

    Tom, we sleeve wells with 4" sch 40 pvc all the time here in western Ct, the 4" inside diameter leaves just enough room for a standard 4" pump (actual size is 3 7/8) to fit inside.


    What I have done is to run my down hole camera into the well to determine where the water is coming in, could be the casing is leaking either at a joint or at the drive shoe, then I run enough 4" pvc in with a "jaswell packer" on the bottom to seal off the water coming in through the leaky casing or drive shoe. The advantage of the jaswell packer is that it can be moved further down the hole if you didn't get the bad water sealed the first time. Sometimes the pitless adapter has to be dug up in order to get the packer down through the casing.