Originally Posted by
valveman
A couple of years ago there was a city in Texas that had a big fire. The fire trucks were sucking on the fire hydrants faster than the city and water lines could supply. The suction collapsed the city water lines in many places. If you suck it down below 0 pressure, you can collapse your lines. A flow switch doesn't care about the pressure and could still be closed as you were creating the negative pressure. A low suction pressure switch will catch before negative pressure.
You can give it a wide bandwidth to stop the cycling from the city pressure coming and going. Set it to shut down at 10 PSI and not back on until the city pressure gets back up to 30 or even 40 PSI. You can also install this switch with a small 1 gallon size bladder tank. If you restrict the size of the opening to this tank and switch, it makes a mechanical timer. ½ a gallon of water has to come in or go out of this tank for the pressure to change from 10 to 30. So the slower you let this water in an out, the more time you have between off and on, and the switch does not bounce the pump on and off. I have one set up this way with a 1/4" poly line running from the main line to the little tank and switch. No switch bouncing!!