    Default Circulation Pump Operating Cost

    This is a technique to heat water with a wood-stove. I would consult a few professional plumbers prior to installing a system like this.
    Question: How do I determine the cost to operate the pump? I'm wondering if it is going to be an unjustified conversion because of pump operating costs.

    Thanks for any input

    http://www.hilkoil.com/Technical.htm
    "Any American who is prepared to run for President should automatically, by definition, be disqualified from ever doing so."
    Gore Vidal.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,374

    Default

    Most circulators are farily small pumps, drawing less than 100W. Taco makes a bunch, and you can view their spec sheets www.tacohvac.com (there might be a hypen between taco and hvac).
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    In the Trades Bob NH's Avatar
    Join Date
    Oct 2005
    Location
    New Hampshire
    Posts
    3,307

    Default

    The pump power is going to be one of the least of your problems.

    The problem with putting a coil in a wood or coal stove is that there is no control of the temperature.

    Water boils at 212 F, meaning that the steam pressure at 212 F equals atmospheric pressure of 14.7 psi absolute.

    At 350 F, which is well within the range of a fire in a wood stove, the gauge pressure is 120 psi. That is much greater than the pressure of your water supply so the steam will force water back into your supply system. In a hot fire of 450 F the pressure will exceed 400 psi and there is considerable danger of bursting copper piping and/or failing solder joints.

    The relief valve will prevent overpressure but that will dump a lot of hot water in an uncontrolled way.

    The temperature/pressure relief valve in a water heater relies on having the hot water at the temperature-sensing stem, which will not be in the hottest part of the wood stove.

    The safety issue is why many residential wood-fired boilers use vented (atmospheric pressure) tanks that can't build up any pressure. You could safely run the water-heater coil through such a tank, but it is not safe to simply put it in the firebox.

    A tankless coil in an oil-fired boiler works because the boiler has a temperature control that limits the heating and the tankless coil is immersed in the water of the boiler.

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by Bob NH View Post
    The pump power is going to be one of the least of your problems.

    The problem with putting a coil in a wood or coal stove is that there is no control of the temperature.

    Water boils at 212 F, meaning that the steam pressure at 212 F equals atmospheric pressure of 14.7 psi absolute.

    At 350 F, which is well within the range of a fire in a wood stove, the gauge pressure is 120 psi. That is much greater than the pressure of your water supply so the steam will force water back into your supply system. In a hot fire of 450 F the pressure will exceed 400 psi and there is considerable danger of bursting copper piping and/or failing solder joints.

    The relief valve will prevent overpressure but that will dump a lot of hot water in an uncontrolled way.

    The temperature/pressure relief valve in a water heater relies on having the hot water at the temperature-sensing stem, which will not be in the hottest part of the wood stove.

    The safety issue is why many residential wood-fired boilers use vented (atmospheric pressure) tanks that can't build up any pressure. You could safely run the water-heater coil through such a tank, but it is not safe to simply put it in the firebox.

    A tankless coil in an oil-fired boiler works because the boiler has a temperature control that limits the heating and the tankless coil is immersed in the water of the boiler.
    Not to mention the endless hours of cutting wood unless you plan on buying it and if you buy it what have you saved.

  5. #5
    DIY Senior Member molo's Avatar
    Join Date
    Sep 2006
    Location
    cold new york
    Posts
    840

    Default

    Quote Originally Posted by Bob NH View Post
    The pump power is going to be one of the least of your problems.

    The problem with putting a coil in a wood or coal stove is that there is no control of the temperature.

    Water boils at 212 F, meaning that the steam pressure at 212 F equals atmospheric pressure of 14.7 psi absolute.

    At 350 F, which is well within the range of a fire in a wood stove, the gauge pressure is 120 psi. That is much greater than the pressure of your water supply so the steam will force water back into your supply system. In a hot fire of 450 F the pressure will exceed 400 psi and there is considerable danger of bursting copper piping and/or failing solder joints.

    The relief valve will prevent overpressure but that will dump a lot of hot water in an uncontrolled way.

    The temperature/pressure relief valve in a water heater relies on having the hot water at the temperature-sensing stem, which will not be in the hottest part of the wood stove.

    The safety issue is why many residential wood-fired boilers use vented (atmospheric pressure) tanks that can't build up any pressure. You could safely run the water-heater coil through such a tank, but it is not safe to simply put it in the firebox.

    A tankless coil in an oil-fired boiler works because the boiler has a temperature control that limits the heating and the tankless coil is immersed in the water of the boiler.

    Hello Bob and thank you for your response regarding safety.

    I am aware of the potential disaster and death that an improperly designed and installed wood heated water system can cause. This particular technique (putting a tube in the firebox) does require alot of attention. Would the use of an aquastat work to insure the water circulates and stays cool enough?

    If this idea is just not feasibly safe, I would consider an "open" system.
    Here is a unit made in vermont that is patent pending and attaches to the outside of the stove, perhaps safer. I would like to know your or anyones opinion on the use of this or other techniques to heat water.

    I have an ample supply of firewood here in the Northeast, and don't mind the exercise to cut it.

    http://www.wipo.int/pctdb/en/wo.jsp?...6&DISPLAY=DESC

    http://cgi.****.com/Hot-Water-Tank-W...QQcmdZViewItem

    Thanks,
    Molo
    "Any American who is prepared to run for President should automatically, by definition, be disqualified from ever doing so."
    Gore Vidal.

  6. #6
    In the Trades Bob NH's Avatar
    Join Date
    Oct 2005
    Location
    New Hampshire
    Posts
    3,307

    Default

    The Aquastat could control circulation but the problem is that the heat must be dissipated or the whole water heater could exceed the safe temperature.

    The Aquastat in a normal boiler controls the temperature of the boiler by controlling the fuel. It turns off all of the fuel when the water in the boiler reaches the controlled temperature.

    A wood stove can be shut down by limiting the air but the temperature doesn't drop quickly.

    An open boiler is safe because it evaporates the water when the temperature reaches 212 F and dissipates the heat with steam. Each pound of steam lost carries away about 1000 BTUs of heat.

    If you put a coil in the stove and connect it to a non-pressurized or low-pressure tank outside the stove, preferably working as a thermosiphon, and then circulate your domestic hot water through a coil in that tank, you could do it safely. The external tank could also supply a circuit for heating the house through low-pressure steam or circulating hot water.

  7. #7
    DIY Senior Member molo's Avatar
    Join Date
    Sep 2006
    Location
    cold new york
    Posts
    840

    Default

    Thanks for the response Bob,

    The thermosipohon is an attractive option. It would eliminate the need for a pump. Do you have any suggestions for finding engineering info. for thermosiphon designs?

    TIA,
    Molo
    "Any American who is prepared to run for President should automatically, by definition, be disqualified from ever doing so."
    Gore Vidal.

  8. #8

    Default

    Molo,
    have you considered adding a large storage tank ? ots a great way to deal with the excess heat from a wood fire.
    www.stsscoinc.com

    Lou

  9. #9
    Computer Programmer Bill Arden's Avatar
    Join Date
    Sep 2006
    Location
    MN, USA
    Posts
    584

    Default

    The key to safety is to make sure that the water loop can dissipate heat faster than the wood stove can heat it. This means that a pump based system is safer since the pump can remove heat faster than a thermosipohon.

    A large tank also helps since it averages out the heat serges that the wood stove can create due to fast burning items.

    In terms of efficiency you would be better off placing the tubing around the box and around the chimney and keeping the fire box hot.
    Important note Ė I donít know man made laws, just laws of physics
    Disclaimer: I'm a big fan of Darwin awards.

  10. #10
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Would placing the relief valve on the inside of the fire box help to control the heat?

  11. #11
    DIY Senior Member molo's Avatar
    Join Date
    Sep 2006
    Location
    cold new york
    Posts
    840

    Default

    Now that is a great idea JW, put the pressure relief valve INSIDE the fire box. Would you warranty that installation please?

    Thanks for the good advice Bill Arden, I have seen someone take an Fuel Oil hot water tank that had a 6" flue. He ran his stove pipe chimney through it, and heated the water in the tank. The water got dangerously hot. He had a thermosiphon set up to take the hot water to a tank above this one. It still wasn't a safe design. I won't do anything until I feel I have a safe, working design.

    Any good advice is appreciated,

    Molo
    "Any American who is prepared to run for President should automatically, by definition, be disqualified from ever doing so."
    Gore Vidal.

  12. #12
    Computer Programmer Bill Arden's Avatar
    Join Date
    Sep 2006
    Location
    MN, USA
    Posts
    584

    Default

    Quote Originally Posted by jwelectric View Post
    Would placing the relief valve on the inside of the fire box help to control the heat?
    No, the heat would cause it to fail

    I wonder what would happen if you ran a pipe from the relief valve so that it wet down the fire. This could be set up as a sprinkler type system.

    Making it so that the fire can't make it too hot is a better idea, but that brings up the question of what happens if the pump fails.

    A relief valve should be used as a way to prevent very bad things from happening when something else fails.

    FYI: I'm playing with concentrated solar power and the heat would melt my copper pipe if the pump stopped.

    Putting a copper pipe in the firebox will work as long as the pump does not fail. If the pump fails you will have water everywhere.
    Important note Ė I donít know man made laws, just laws of physics
    Disclaimer: I'm a big fan of Darwin awards.

  13. #13

    Default

    I happened to hit this discussion through scanning the web...

    I've been looking for an installed system of this type for some time to see how it would be done.

    My idea would be for a new-home application where heat would be needed, but not something that may be absolutely crucial... In my case, a smaller cabin in a forested area near the California coast where temps are typically not much lower than the low 40's with no typical freezing, icing, or snow...

    The system would have a sealed (outdoor input air only) thermal-fireplace (say, soapstone) with a water-heating coil inside the the firebox. The heated water from the fireplace would recirculate through an insulated hot-water storage tank by way of a pump. Once the fire was out, and the fireplace was loosing its thermal kick, the stored hot water would then be circulated through a radiant floor heating system (pex in slab) to further warm the house.

    This could be a closed system with antifreeze, pressure relief valves, expansion tank, etc....

    The obvious concerns are pressure and over-heated water--mostly from pumps failing. But some emergency options have been mentioned:

    -- Dousing the fire.

    -- If the water in the storage tank gets too hot, then it would sound an "alarm" and the radiant-heat floor pump kicks on to use the house slab as a kind of radiator to cool the tank and let you know to ease up on the fire.

    -- Additional water could be added to the tank to cool it.

    -- The addition of a small solar water heater panel could be added to the roof to preheat the storage tank (if needed), which could also radiate unwanted heat.

    Any ideas or criticisms? All input welcomed.