Macerator toilet.

Users who are viewing this thread

rice9923

New Member
Messages
2
Reaction score
0
Points
0
I am installing a macerator toilet in my basement. In North America this type of unit has to be vented. Can this application be vented with a automatic vent?

thanks
 

Clayton

Plumber
Messages
123
Reaction score
0
Points
0
Website
www.facebook.com
Macerating Toilet

No....

No air admittance valves or mechanical vent allowed on the pump basin. It has to connect with existing vents in the house or be piped seperatly to the outside. Be sure to block any other vents or carbon filter vents in the basin for use outside of the USA.
 