This is done quite frequently in situations like yours or when customers want to remote the cond units from the house because they are unsightly or because of noise. At a minimum we normally add a liquid line solenoid at a location close to the evap coil. When the compressor comes on the solenoid comes on. when the compressor is off the solenoid closes and stopping refrigerant flow and minimizing the migration of refrigerant and oil to the lowest and coldest spot which usually is underground. This works well on short runs. If it was a long run we would add an accumulator. As for the covering/protection we use the corrugated drainage tubing ( without the holes in it ). It is 4" and flexible and easy to work a lineset through. Insulate both lines and seal it as best as possible to prevent any water from laying in there