    Default Hot water in Cold line/basement rough-in

    I had plumbing roughed-in for a full bath down in the basement a few months ago. When I run the kitchen and upstairs bathroom faucets, we get hot water in the cold line for a few moments. I checked the rough-in lines in the basement tonight and the hot and cold water lines going through the new bathroom are both quite hot. I have a shower that is rough-ed in as well. Could this be the mixing point for the hot and cold water? How do I take care of this as I might not want to finish the rough-in for a couple more months. Any advice is appreciated. Thanks, Dave

  2. #2
    Plumber krow's Avatar
    Join Date
    Feb 2008
    Location
    Ontario, Canada
    Posts
    906

    Default

    Quote Originally Posted by zerolast View Post
    I have a shower that is rough-ed in as well.
    What type of valve do you have roughed-in?

  3. #3
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    I bet a delta without the cartridge installed yet...

  4. #4
    DIY Junior Member zerolast's Avatar
    Join Date
    Mar 2008
    Location
    Columbus, Ohio
    Posts
    7

    Default

    Yes, it is a delta with just a gray knob where I assume the cartridge will go. Is there a temporary fix without finishing this off?
    Last edited by zerolast; 03-03-2008 at 03:19 AM.

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default Delta

    NO. it is designed to pressurize both hot and cold lines in a new situation where the hot water heater is probably not installed, and the two systems may not be connected together any other way.

  6. #6
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    Thats some crystal ball huh? There seems to be a rash of these Delta rough in hot/cold cross connections lately. It seems to be a common installer error. You either need to install the cartridge or, put valves in the supply pipes to the Delta valve and turn them off.

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default Delta

    I suppose the idea is that it is either going into a new construction where the crossover is helpful, or a remodel where the trim is usually installed almost immediately. The one thing Delta does not want is for the installer to put it in, turn on the water and assume there is no leak, but not have water pressure on the hot side.