Hot Water heater sizing question

Users who are viewing this thread

Ron in SC

New Member
Messages
80
Reaction score
0
Points
0
Location
South Carolina
I need to install water heater for detached garage, it will have to be electric.

How big a tank to I need? It will need to supply hot water to following:
-front loader washing machine, used only to wash items used in connection with use of garage
-sink
-shower; which will be used infrequently
-outside spigot; also used infrequently
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
A 30 gallon would be fine for the WM and shower, although a 40 doesn't cost much more.

A hose bibb will suck an 80 gallon dry in about 4 minutes!
 

Ron in SC

New Member
Messages
80
Reaction score
0
Points
0
Location
South Carolina
A hose bibb will suck an 80 gallon dry in about 4 minutes!

I do have a spigot next to it that is regular water, if I do use the hot water to wash really dirty stuff like boat it sounds like I should make a connnection between the two so I can mix the hot water with the cold.

Also what do you think about those hot water heaters that have can be set for a few different modes. One of the house hot water heaters has that it's a Whirlpool and has this thing on top that say energy smart. Are they just a gimmick? Maybe one of those would be good in the garage too.
 

Squ1rrel

New Member
Messages
69
Reaction score
0
Points
0
Location
Texas
Those energy smart panels are supposed to track usage and only keep water hot during the times you most use it...not sure how well it would work if you use different amounts at changing times. Plus it's a Whirlpool..with all the problems with their gas WH's, I'd be leery of their electrics too.
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
One of the house hot water heaters has that it's a Whirlpool and has this thing on top that say energy smart. Are they just a gimmick? Maybe one of those would be good in the garage too.

"Energy smart" on an electric water heater is a gimmick. They have such good insulation, and such poor recovery rate, that controlling the heating on a 24 hour cycle would be a hopeless exercise.

The only "energy smart" that would mean anything would be if you were getting a special rate from the power company for off-peak power. If that is the case there should be a power company clock system that would allow them to shut off the lower element during peak (high rate) times.
 

Herk

Plumber
Messages
545
Reaction score
0
Points
0
Location
S.E. Idaho
50 gallon may be as cheap or very nearly the same price as a smaller heater. Paying more for efficiency is a very good idea - better insulation saves money. Paying for silly electronic gadgets and hype is not a good idea. (Not yet, anyway. Maybe someday they'll actually implement such things effectively.)
 

Ron in SC

New Member
Messages
80
Reaction score
0
Points
0
Location
South Carolina
A 30 gallon would be fine for the WM and shower, although a 40 doesn't cost much more.

Is it cheaper as far as electricity goes to use a smaller tank, since it should take less electricity to keep less water hot?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Not necessarily. The exterior surface area difference between different size water heaters isn't quite linear, so a bigger WH has less exterior surface area to radiate out heat from than a smaller one. The quantity and quality of insulation makes a big difference. WIth an electric WH, you have nearly 100% efficiency in heating, but your standby loss is determined by the quality of the insulation and the area that acts like a radiator.
 

chawk

New Member
Messages
1
Reaction score
0
Points
0
Location
Charlottesville VA
I'd go with the 50 gallon, you must have a nice setup, and or income to have a detatched garage with a washer and dryer just for the garage. :) but hey more power to you.
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,537
Reaction score
357
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
get the 50 and install a breaker switch.

Get the 50 gallon and put the blanket on it...

Stay AWAY from that Energy smart heater...,,
it is a piece of junk and will eventually give you troubles
http://www.weilhammerplumbing.com/galleryi/

Get a GE from HD


Now if you really want to save energy in the garage,

install a breaker or a breaker junction box with a lever
right next to the water heater....
and just turn the water heater on only when you need to
on the weekends or an hour before the action begins....
instead of heating the water 24 hours a day.....

it will literally heat up in about a half hour ..
.
 
Last edited:

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
Now if you really want to save energy in the garage,
install a breaker or a breaker junction box with a lever right next to the water heater....
just turn the water heater on only when you need to
on the weekends or an hour before the action begins....
instead of heating the water 24 hours a day.....
it will literally heat up in about a half hour ..

Sounds like the perfect environment for legionella!
The water should be in the prime growth zone for about all week!


On a lighter note I would suggest this sillcock for hot/cold water mixing. Just using a wye hose cold be a cross connection that among other things could crack a toilet. http://www.moen.com/products/HC400508

HC400508.jpg
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
I do not advocate turning off the heat on a water heater. This will increase the danger if Legionaires desease.

The biggest single threat from tepid water is probably legionella.

70 to 80 °C (158 to 176 °F) - Disinfection range
At 66 °C (151 °F) - Legionellae die within 2 minutes
At 60 °C (140 °F) - Legionellae die within 32 minutes
At 55 °C (131 °F) - Legionellae die within 5 to 6 hours
50 to 55 °C (122 to 131 °F) - They can survive but do not multiply
20 to 50 °C (68 to 122 °F)- Legionellae growth range
35 to 46 °C (95 to 115 °F) - Ideal growth range
Below 20 °C (68 °F) - Legionellae can survive but are dormant


http://en.wikipedia.org/wiki/Legionella

Many of the states and at least some of Canada are now requiring water heaters set at 140 Degrees F and a tempering valve on the outlet to lower the water temp to 120 Degrees F. I would expect that this will be a code requirement everywhere before long.

Have a look see at this link... http://www.cashacme.com/legionella_main.php

 
Last edited by a moderator: