Thread: Conduit Fill Question

  1. #16
    Aspiring Old Fart, EE, computer & networking geek Mikey's Avatar
    Join Date
    Nov 2005
    Location
    Central Florida
    Posts
    2,685

    Default

    I couldn't begin to count the number of cabinets, boxes, etc., I've seen with cables coming in from all sides and the back through conduit of one sort or another.

  2. #17
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by Mikey View Post
    I couldn't begin to count the number of cabinets, boxes, etc., I've seen with cables coming in from all sides and the back through conduit of one sort or another.
    I drive down the road every day at the posted speed being passed by a lot of people.

    Does this mean that all those people are right?

  3. #18
    I&C Engineer (mostly WWTP) Lakee911's Avatar
    Join Date
    Aug 2005
    Location
    Columbus, OH
    Posts
    1,328

    Default

    Quote Originally Posted by Speedy Petey View Post
    Um....no. This is not a legal solution, especially if you are doing it to gain fill space.

    Do you have a code reference as to why this is illegal? Wire inside romex is thhn and both the shiething and the conduit serve as to protect the wires. From my googling, I've seen both ya and nah on it.

    Jason

  4. #19
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by Lakee911 View Post
    Do you have a code reference as to why this is illegal? Wire inside romex is thhn and both the shiething and the conduit serve as to protect the wires. From my googling, I've seen both ya and nah on it.

    Jason
    The conductors in Non Metallic Cable is NOT THHN it is only rated at 90 degrees.

    312.5(C)(e) The cable sheath is continuous through the raceway and extends into the enclosure beyond the fitting not less than 6 mm (ľ in.).

  5. #20

    Default

    NM-B cable, commonly called NM is rated 90 degrees, the wire inside NM is not THHN (look at the wire; it has no neoprene covering) but it is rated 90 degrees. But look at 334.80, its ampacity is per the 60 degree table, except for derating. Old romex that is not labeled NM-B is rated 60 degrees.

  6. #21

    Default

    Note to jwelectric: "Exception: Cables with entirely nonmetallic sheaths shall be permitted to enter the top of a surface-mounted enclosure.... "(using 18 inch to 10 ft pieces of conduit, sealed and under certain other conditions )
    This is an exception to the cable clamping rule above it. It tells us we are permitted to build under a certain conditions. It does not PROHIBIT all other installations.
    Obviously NM cables installed within a conduit system can enter the side and bottom of the box as long as all appropriate Code rules are followed.
    Therefore, if you install a junction box at the bottom end of the 2" PVC then you will be converting to a conduit with wire(or cable) in it wiring system. This will make your installation not subject to the cable clamping rule. And not subject to the "top of cabinet" exception to the cable clamping rule.
    Boxes with conduits entering top bottom sides and back are not breaking the rules, unless they are short, open ended pieces of conduit with NM installed.
    Last edited by ked; 03-04-2008 at 06:05 AM.

  7. #22
    Aspiring Old Fart, EE, computer & networking geek Mikey's Avatar
    Join Date
    Nov 2005
    Location
    Central Florida
    Posts
    2,685

    Default

    Quote Originally Posted by jwelectric View Post
    I drive down the road every day at the posted speed being passed by a lot of people.

    Does this mean that all those people are right?
    Certainly not all of them, but probably most of them. There's a 6-lane divided highway near me with a 35mph speed limit posted. If you want to have some fun, drive it at 35mph.

    "Right" is not always defined by laws or codes, which were not all written by people with an adequate command of knowledge, reason, logic, or English.

  8. #23
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by Mikey View Post
    "Right" is not always defined by laws or codes, which were not all written by people with an adequate command of knowledge, reason, logic, or English.
    Help me to understand just what you are saying here, please.

    Are you saying that just because someone is driving over the posted speed limit it gives everyone else the right to do the same thing?

    Should this type of thinking be used when raising children? A bunch of kids at school is picking on my kid so I just tell my kid that it is alright because one group of kids over rule the feelings of one.

    Come on now Mikey stand up for the laws that we tax payers have spent so much money to have enacted. Donít join the crowd of misfits just so you can fit in but instead set an example for those who look up to you and do as out leaders say we are to do and drive at the posted speed.

  9. #24

    Default

    This traffic analogy is going overboard. Obviously, traffic rules are often broken in emergencies and to promote safety. These are one-time instances. Also, if a speed limit is too low or too high for safety, have your city council change it.
    We are building mechanical systems that will last for 50 or more years. This is why the rules are important.
    Generally, the electrical Code is carefully written. Our problem with the conduit and cable section is that we are not reading carefully or are out of context.
    See my solution above. The real arguments are about local AHJs interpretations of the Code.

  10. #25
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by ked View Post
    Note to jwelectric: "Exception: Cables with entirely nonmetallic sheaths shall be permitted to enter the top of a surface-mounted enclosure.... "(using 18 inch to 10 ft pieces of conduit, sealed and under certain other conditions )
    This is an exception to the cable clamping rule above it. It tells us we are permitted to build under a certain conditions. It does not PROHIBIT all other installations.
    Obviously NM cables installed within a conduit system can enter the side and bottom of the box as long as all appropriate Code rules are followed.
    Therefore, if you install a junction box at the bottom end of the 2" PVC then you will be converting to a conduit with wire(or cable) in it wiring system. This will make your installation not subject to the cable clamping rule. And not subject to the "top of cabinet" exception to the cable clamping rule.
    Boxes with conduits entering top bottom sides and back are not breaking the rules, unless they are short, open ended pieces of conduit with NM installed.

    In ***.10 and .12 of all the cable articles outlines the uses permitted and uses not permitted for the installation. Article 334 mandates the rules for the installation of NM cable.

    ***.22 of raceway articles will mandate the installation of conductors in that raceway. Letís use PVC for an example;
    352.22 Number of Conductors.
    The number of conductors shall not exceed that permitted by the percentage fill specified in Table 1, Chapter 9.
    Cables shall be permitted to be installed where such use is not prohibited by the respective cable articles. The number of cables shall not exceed the allowable percentage fill specified in Table 1, Chapter 9.

    When dealing with junction or outlet boxes 314.17 mandates the installation of cables and the requirement to secure the cable to the box. 314.17(B) the rule to allow the installation of a cable to be installed in a raceway for protection is allowed as outlined in 300.15(C).
    These rules will allow the raceway and cable to come into the box from any and all directions.

    BUT

    Article 312 regulates the installation of conductors in enclosures such as panels. 312.5(C) is the rule for installing NM to a panel. When installed in a conduit the exception allows the installation as long as the installation follows ALL of the criteria outlined in the exception.

    I agree that this rule is not enforced as it should be but it is still the rule.
    When installed either in a raceway or as an open cable in ALL installations the sheath of the cable MUST enter the enclosure no less than ľ inch.

  11. #26
    Aspiring Old Fart, EE, computer & networking geek Mikey's Avatar
    Join Date
    Nov 2005
    Location
    Central Florida
    Posts
    2,685

    Default

    Actually, I do drive at the posted speed, which I've found to be a foolproof way of avoiding speeding tickets. I've only been rear-ended once while doing so, which I think is a miracle. People have been killed in our area by stopping for red lights.

    As for all the money we've spent to get these laws enacted, I think we've gotten a lousy deal. At least I don't live in any of the states where their learned legislatures actively considered changing the value of pi to something else, either easier to use, or based on biblical text.

    Having said all that, I agree with Winston Churchill, who is alleged to have said that democracy is the worst form of government except all the others that have been tried.

  12. #27
    Aspiring Old Fart, EE, computer & networking geek Mikey's Avatar
    Join Date
    Nov 2005
    Location
    Central Florida
    Posts
    2,685

    Default

    Quote Originally Posted by ked View Post
    Also, if a speed limit is too low or too high for safety, have your city council change it.
    Good luck.

  13. #28
    DIY Member arfeller's Avatar
    Join Date
    Aug 2007
    Location
    Port Angeles, WA
    Posts
    77

    Default

    Crap.

    From this point forward i'm sticking to yes and no questions

    Thank you all for the input. Some real good suggestions here and now i have a good path forward.

    Thank you.

  14. #29
    I&C Engineer (mostly WWTP) Lakee911's Avatar
    Join Date
    Aug 2005
    Location
    Columbus, OH
    Posts
    1,328

    Default

    Ok. I stand corrected.

    Jason

  15. #30
    DIY Member Kiril's Avatar
    Join Date
    Jun 2007
    Location
    Sacramento, CA
    Posts
    87

    Default

    Somewhat related question, do the same fill restrictions apply to low volt?

    Also, are there any restrictions with regard to what type of conduit that can be used to run low voltage cables?