The inspector is quoting 408.16(F) Back-Fed Devices.
Plug in type overcurrent protection devices or plug-in type-main lug assemblies that are backfed and used to terminate field-installed ungrounded supply conductors shall be secured in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panel.
so basically what this means is that if you are backfeeding a breaker to supply a panel you need a means of holding that breaker in place.... THis would only take place if you bought a main lug panel and wanted a MAIN disconnect...