    Default Sprinkler zone wouldn't stop

    Have a timer with 5 zones active. One of the zones would not stop this morning. Tried to stop sprinklers manually by turning off the timer, but water would not shut off. Had to turn off water to irrigation system to stop the sprinkler. Is this most likely a problem with the anti-siphon valve getting stuck open? Or a problem with the timer? Sorry for the lack of details. Thanks much for your help.
    Attached Images Attached Images  
    Last edited by maddog; 03-03-2008 at 03:43 PM.

  2. #2
    Engineer maddog's Avatar
    Join Date
    Aug 2006
    Location
    near San Jose, CA.
    Posts
    131

    Default

    I'm thinking it's the anti-siphon valve. Came home and unplugged timer - turned on water and the sprinklers came on again. The solenoid looks a bit corroded and probably has dirt or something inside. Will replace and see what happens.

  3. #3
    Sprinkler Guy Wet_Boots's Avatar
    Join Date
    Mar 2007
    Location
    Metro NYC
    Posts
    798

    Default

    Unplug a timer to be certain it isn't the problem.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default valve

    IT is inside the valve. Something is torn, broken, or stuck inside the valve.

  5. #5
    Rancher
    Guest

    Default

    The valve operates by that solenoid opening a bypass orifice, which causes the main valve to spring open. If you get a grain of sand in the solenoid-orifice seat, the valve will not turn off.

    Solution, unscrew the solenoid, clean it out.

    Rancher

  6. #6
    Engineer maddog's Avatar
    Join Date
    Aug 2006
    Location
    near San Jose, CA.
    Posts
    131

    Default

    Great - thanks much ... will give it a try.

  7. #7
    Engineer maddog's Avatar
    Join Date
    Aug 2006
    Location
    near San Jose, CA.
    Posts
    131

    Default

    Unfortunately, removing/cleaning the solenoid didn't do it. A replacement solenoid at HD was almost as much as a new valve, so I replaced the valve - and I'm back in business. Thanks much for the input. -dog