    Have an apartment with a sweating toliet. The tank and bowl are both sweating. Replaced flapper valve and did a color test. No leakage from the tank into the bowl. Any other ideas out there?

  2. #2
    Plumber krow's Avatar
    Join Date
    Feb 2008
    Location
    Ontario, Canada
    Posts
    906

    Default

    Get air conditioning or,

    Turn down the heat in the apt. or

    a new toilet with insulated tank

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,428

    Default

    They do make mixing valves for toilets that mix warm and cold to raise the incoming water's temp above the dew point. This is more of a problem on a toilet that is flushed often. If the toilet is not one of the newer 1.6 or less toilets, changing to one of them may help. The old ones often empty the entire tank. Therefore, you're replacing all of the water with colder stuff, and it may run long enough to be very cold. The new ones usually only dump 50-60% of the water, so there is some room-temperature water to mix or temper the incoming cold, and since you don't run as much, it may be warmer all by itself. I have no experience adding insulation to a tank, in fact, I've not seen one of the factory installed insulated tanks, so I can't comment on if this is even possible with an older tank.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4

    Default

    When a toilet sweats, it's really the water from the room that's sticking to it because of the difference in temperatures.

    Our code requires either a window or a fan to remove moisture from a bathroom. This is important because of the water damage and mildew that can occur. The best fix for this would be to use a ceiling fan to remove the moisture from the room.

    As to insulated tanks - I've never found them to work all that well.

  5. #5
    DIY Senior Member Mike Swearingen's Avatar
    Join Date
    Jan 2005
    Location
    On Albemarle Sound In Northeastern NC
    Posts
    621

    Default

    Yep. The problem is condensation on the toilet from warm, moist air in the bathroom, not a leak.
    You can add a hot water mixing valve, add an after-market insulation kit in the tank, add a terry cloth cover on the tank, etc., but the best solution is to run a fan (ceiling exhaust or recirculating) to help dry out the bathroom whenever someone takes a bath or shower or uses hot water in the sink.
    Good Luck!
    Mike

  6. #6
    Plumber gear junkie's Avatar
    Join Date
    Feb 2008
    Location
    Virginia Beach, IPC country
    Posts
    67

    Default

    Pressure assisted toilets don't sweat either but I think the previous suggestions of a toilet cover is the most feasible.