Thread: pressure tank recovery???

  1. #1

    Default pressure tank recovery???

    If I run the shower, the water pressure will gradually drop on the gauge from 60 down to 40, then the switch contacts close and the needle flickers a bit then just drops off to zero for about 8-10 seconds then jumps back up to 40 and pressure builds back up and all is good, until the next time. I have properly checked the tank pressure 38-40 and top end 60. Of corse the actual water in the shower reflects how I described the gauge, is ok graduely drops then nothing, then back. I have a submersable well pump about 600 ft down with plenty of water. Please tell me I dont have to have it pulled up again. Its only 4 yrs old and I just had to have it pulled for a broken wire at the pump, from a chafe due to it torqueing when turning on. That was late December and 600 bucks. Any ideas???

  2. #2
    Previous member
    Join Date
    Jul 2005
    Location
    Riverview, Fl.
    Posts
    4,540

    Default

    First of all, if the wire were properly taped to the droppipe, there wouldn't be any skinned wires.

    You either have too much air in the tank (which has to be checked with no water pressure in the system and the pump off) or your pressure switch is not seeing the pressure drop as quick as it should because of a plugged pipe or tube.

    More on Bladder Tank FAQ's

    bob...

  3. #3

    Default

    Yea who ever instaled the pump new didn't use a stand off, thats why I had the chafe.
    I just baught a new switch and will change and post back.
    I have already properly checked the tank pressures, and switch settings.unless my tire gauge is off.

  4. #4
    Previous member
    Join Date
    Jul 2005
    Location
    Riverview, Fl.
    Posts
    4,540

    Default

    Changing the switch may not cure the problem. The switch is turning on and off the pump, so it's working. It's the fact that the water pressure isn't getting to the switch quick enough because of a restriction in the plumbing feeding the switch. That is what you need to check.

    I'm not sure what a stand off is. Maybe a Torque Arrestor? I don't recommend their use either.

    bob...

  5. #5

    Default

    Stand off, I ment something to tie the wires to at the pump.

  6. #6
    Previous member
    Join Date
    Jul 2005
    Location
    Riverview, Fl.
    Posts
    4,540

    Default

    The best place for them is tightly taped to the droppipe.

    bob...