Hello,

I'd like to pressure test my vertical spa installation (lots of fittings). It has held 40 PSI for 4 hours.

What is the recommended air pressure and set time for air testing copper? The valves are installed. I did not want to risk over pressurizing the valves.

Thanks,
Steve
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
test

The valves are rated for 150 psi working pressure and no common compressor is allowed to exceed about 125 psi, so you couldn't damage the valves.
 