Page 1 of 2 12 LastLast
Results 1 to 15 of 24
Thread: "retainers" for breakers?
    Default "retainers" for breakers?
    Hope you guys can help me here, as the "pros" at the electrical distributor shop were stumped.
    At my final a couple weeks back, the inspector was darn fair. He found a few things to fix, and this is the last one...
    I have two "main" panels for the house, both of about the same size. One on the outside, then one on the inside (that's fed from the one on the outside).
    outside
    inside
    On the inside one, there's a feed - dual breaker - going to a smaller breaker box that's dedicated to my power tools (so I could lock it out if I wanted to).
    dual breaker, pulled off, showing the retainer the electrical place sold me.
    The inspector says I need some kind of retainer holding this dual breaker down, so that when you flip it off, it won't pull out of the panel (funny thing though - he didn't mention the same requirement for the ones for the oven just adjacent to it).
    My outside panel has one of these retainers- for the MAIN power breaker(s) - 200A.
    Here's the one on the main panel outside. There's screws
    BUT, on my inside panel, there's nothing "behind" the breaker that will allow me to fasten it down.
    Any suggestions on this? The "box number" of my inside panel is BXH26/K if that helps. Square D's website is where I found that gold colored bracket (that doesn't fit), and otherwise was no help.
    Shawn
    Electrician Chris75's Avatar
    Aug 2007
    Litchfield, CT
    The inspector is quoting 408.16(F) Back-Fed Devices.
    Plug in type overcurrent protection devices or plug-in type-main lug assemblies that are backfed and used to terminate field-installed ungrounded supply conductors shall be secured in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panel.
    so basically what this means is that if you are backfeeding a breaker to supply a panel you need a means of holding that breaker in place.... THis would only take place if you bought a main lug panel and wanted a MAIN disconnect...
    Aug 2007
    Litchfield, CT
    You dont even need this since your NOT backfeeding a breaker...
    Jun 2007
    NY State, USA
    What Chris said!
    Also, DO NOT (!!!!) attempt to install this device. Like you said, there is NO place to screw it to. If you try you'll quickly find the live buss bars.
    The outside panel is a "one sided" panel if you notice. This is why there is a place it install a back-feed breaker hold down.
    Great info guys, but I'm afraid I actually am backfeeding (I don't really know the definition).
    The breaker he's saying needs to be retained leads to another small panel in the garage, that has 4x 20A breakers in it (for my tools).
    Having said this, does your previous statements still hold true, that I DON'T need the hold down?
    I agree, there's no easy way to hold it down, unless I rig something (a little metal tab?) to the front of the panel cover to secure it.
    Sincere thanks for the advice gents.
    -Shawn (homeowner who's contractor skipped out on him and who's left to finish the job himself)
    Jun 2007
    NY State, USA
    This breaker DOES NOT need to be retained. This is NOT a "backfeed" breaker.
    If the AHJ says it does he is most certainly incorrect.
    I&C Engineer (mostly WWTP) Lakee911's Avatar
    Aug 2005
    Columbus, OH
    Backfeeding means that you're bringing in power through a circuitbreaker on the bus (and not a dedicated main CB for the panel). In your case if you were backfeeding you would have a power source on your subpanel for your tools and using that to power the panel in question.
    Ask the inspector to clarify his request. Attempting to install that without a suitable method of doing so would likely violate other codes as well.
    Does this 4x20A smaller panel have a main breaker or just lugs?
    If it HAS a main, THAT is the one that would be required to be screwed in place or changed to lugs.
    I still don't really understand backfeeding.
    Alectrician - Your question: "Does this 4x20A smaller panel have a main breaker or just lugs?"
    If I understand this right, it just has lugs. Meaning, there's no breaker in that panel that cuts off all 4 of the 4x20s. There's just the 4x20s in there.
    So, what specifically should I tell my inspector? Telling him "But those guys over at Terry Love said that the hold-down isn't required" is not going to get the job done, if you know what I mean...
    Looking here under "B" it sounds like what I have IS backfed.
    http://books.google.com/books?id=hot...Lq2A#PPA168,M1
    I'm very confused.
    Electrical Contractor jbfan74's Avatar
    Jun 2007
    Newnan, GA
    Quote Originally Posted by shawnharper View Post
    If the subpanel just has lugs, and no main breaker, then you do not have a backfed breaker. If it had a main beraker, you would not have a backfed breaker
    If you used a breaker in the normal position in the panel, to feed that panel, then you would have a backfed breaker.
    Yes I am A Pirate-Jimmy Buffett
    In the Trades Bob NH's Avatar
    Oct 2005
    New Hampshire
    I'm very confused.
    It is very easy to become UNCONFUSED in this matter.
    If the breaker is energized through the STABS that mate with the bus bars, IT IS NOT A BACK-FED BREAKER and DOES NOT need to be fastened in place.
    If the breaker IS ENERGIZED BY THE WIRES COMING TO THE BREAKER, so that if you pulled the breaker out of the panel the STABS connecting to the bus bar would be hot, THEN IT IS A BACK-FED BREAKER AND MUST BE FASTENED IN PLACE SO IT CAN'T BE REMOVED AND EXPOSE HOT STABS.
    A MAIN BREAKER is fed by wires, and therefore it is a back-fed breaker, and is ALWAYS fastened down.
    A subpanel can be any of 3 configurations.
    1. A panel with a standard main breaker in the usual main breaker position, to which the incoming hot wires are connected. The MAIN BREAKER in such a panel is always fastened down BY DESIGN.
    2. A MAIN LUG panel where the incoming leads are connected to large terminals that are connected to the bus bars of the panel. There is no breaker to disconnect the power from the bus bars at that panel and the conductors coming to that panel are protected by a standard breaker (not back-fed) at the panel where the conductors receive power.
    3. A MAIN LUG panel where the power coming TO the panel is connected to a circuit breaker in that panel that supplies power to the bus bars of that panel. THAT CIRCUIT BREAKER IS A BACK-FED BREAKER and must be fastened in place to prevent it from being inadvertantly removed which could expose someone to the hot stabs of the breaker.
    A BACK-FED breaker is sometimes installed in a panel, interlocked with the main breaker, for connecting an emergency generator. When such a breaker is used, that breaker must be fastened in place. Square-D sells a special kit that is used in that application.
    Aug 2005
    Columbus, OH
    Does this help? Is that subpanel backfed or main lug?
    Jason
    Aug 2005
    Columbus, OH
    Why does the main have four breakers?
    Oct 2005
    New Hampshire
    That is a Main Lug panel. I can see the ends of the feed conductors poking out through the main lugs at the top of the picture.
    The breaker that is half-out near your fingers is the one that is feeding another subpanel or other load. It is NOT a backfed breaker and doesn't need to be fastened in place.