Another Hammer arrestor question

Users who are viewing this thread

MikeyBiz

New Member
Messages
4
Reaction score
0
Points
0
I'm installing a new shower thermostatic valve and 1/4 turn volume control.

The old mixing valve had air chambers on the hot and cold inlets. Now that I have separate valves for temp and volume where ideally should the arrestor be placed? 1 arrestor on each hot and cold inlet or 1 at the volume control?
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
arrestors

The "water hammer" will occur at the volume control, but putting the arrestors on the hot and cold lines to the valve should minimize the problem
 