Installing Noritz 931 and read the first vertical run cannot exceed 3'..if you add a horizontal section and then go vertical again that ok.

Any reason for this...does too much vertical venting cause suffocation of unit?
 

billhayton

New Member
Messages
10
Reaction score
0
Points
0
you guys are good...

Makes sense the condensate accumulation is not something noritz or anyone else wants running back to unit.