Thread: How's this DWV?

  1. #1

    Default How's this DWV?

    Looking for input on my DWV for 3 lav's.
    Planning on everything being 2 inch cpvc. Assume 1/4 slope for the horizontal drain.
    Questions:
    1. The 90 elbow will be in a stud wall. Will that work?
    2. Do I even need the vent for the double lav?

    Name:  3lav1.jpg
Views: 456
Size:  19.1 KB

    Name:  3lav2.jpg
Views: 461
Size:  21.4 KB

    Name:  3lav3.jpg
Views: 535
Size:  26.7 KB

    Thanks,
    Amy

  2. #2
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    Close but no cigar! On the 2 closest to the verticle drop you have constructed an s-trap. Review your use of horizintal sani-tees.

  3. #3
    Master Plumber Dunbar Plumbing's Avatar
    Join Date
    Apr 2005
    Location
    Northern Kentucky/Greater Cincinnati Area
    Posts
    2,943

    Default

    The furthest fixture on the drawing is fine only if that vent is 42" up before it goes horizontal.


    The two lavs need to be vented off tees, combined on the vents and go horizontal as one and on up. That involves 42" or higher as well.
    Read what the end of this sentence means.

  4. #4
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    All the vents must be 42" above the floor before they go horizontal.

    The fixture drains must connect to the main with a wye and 45, not the santee shown.

  5. #5

    Default OK, let's try this again. SLightly different Design

    Horizontal vents will be at least 42" above floor or 6" above flood level of the lav.

    Is the 90 Ell in the wall going to be OK?
    Name:  3lav1.jpg
Views: 405
Size:  20.6 KB

    Name:  3lav2.jpg
Views: 392
Size:  18.0 KB

    Name:  3lav3.jpg
Views: 402
Size:  20.7 KB

  6. #6
    Consultant cwhyu2's Avatar
    Join Date
    Aug 2007
    Location
    Cincinnati OH
    Posts
    1,330

    Default

    Looks good to me.Eccept showervent should same hight as lav vent.
    Last edited by cwhyu2; 01-24-2008 at 10:20 AM.

  7. #7

    Default

    Thanks. That is actually a third lavatory. But I will make all the vents the same height.

  8. #8
    Consultant cwhyu2's Avatar
    Join Date
    Aug 2007
    Location
    Cincinnati OH
    Posts
    1,330

    Default

    Your welcome . thougt was a shower pipe it like the other two good to go.

  9. #9

    Default

    the 90's will work in this scenario, the drawings look good, only the numbers for pitch, height, minimum, and maximum are left out.

  10. #10
    I&C Engineer (mostly WWTP) Lakee911's Avatar
    Join Date
    Aug 2005
    Location
    Columbus, OH
    Posts
    1,328

    Default

    I see some offset joints. Might get a clog there