The supressor I have on my panel specifically states in the installation instructions that it must be on its own breakers (either one 220 or two 110 on separate legs).
Am I allowed to double lug (a circuit breaker) for a hardwired secondary surge arrestor?
Considering the fact that the main disconnect is a suitable overcurrent protection device, I could connect the device to the bus bar lugs. The wire size is too small, so how could I fit a #12 wire into a lug designed for something like #1 wire?
Are wire connectors allowed in a panel? I'm replacing a panel and would like to know how to lengthen existing wires if the connectors are not allowed.
Panel is mounted against the wall and the ceiling is low (6.5 or 7ft). Can I bundle the cables (with wire wraps) coming in overhead through one large 2in. knockout and through one cable clamp, or must I bring them in seperately, in conduit? The distance to the ceiling will only be a few inches.
If I mount a 3/4" piece of plywood directly on the masonary block wall with powder actuated fasteners, will 3/4" long fasteners in the plywood alone be adequete to carry the weight of the panel?
Thanks,
Jason
What did the instructions that came with the surge protection say?
and no, you cannot have two wires under one screw...
It didn't say anything about dedicated breakers on the instructions.
I thought I couldn't have two wires under one screw but an electrician told me otherwise (not that it makes it right). He's a friend, so I didn't want to ask for a code reference.
Jason
All of my new breakers have connections that are designed for one or TWO wires. You can tell if the connection has a small plate under the screw with a place for a wire on each side of the screw.
If your surge protector has wires coming from it and no terminals for mating to the lugs of the panel, then it is made to be wired into a circuit. I would just follow the instructions.
Wire nut connections in the service panel are PERMITTED if there is room, and there is in any modern service panel.
Sure you can...if the breaker is designed/rated for two conductors ie. SquareD QO style.
Ok. Well, that's the panel in question.
What do you all think of the other questions?
What you can't / shouldn't do is put 2 different size wires on the same breaker like taking a #12 and #14 wire and putting it on a 15A breaker. I have found a few situations like this and the #14 becomes loose because of uneven applied torque due to the wire size difference.
[QUOTE=Lakee911;119757]
No you can only have 3 cables in each knockout. Table 310-16. Unless you de-rate them.
I dont like using PAFs I have seen too many services hung up by the riser because the pins come out. I would use tapcons they have never let me down.
Well, you're a few days late, since I already used the pins! I put in seven 1-1/2" pins. I don't think it's going anywhere. I'll keep an eye on it. I'll add tapcons if they start to move.
Jason
[quote=lampman42;122519]I would use a short piece of 2" RNC. Then Chapter 9 applies, not 310-16 (300.17 FPN, 352.22). The computation is not simple, depends on the number and size of conductors and types of insulation, and does not apply anyway to "sections of conduit or tubing used to protect exposed wiring from physical damage." (Note 2 to Table 1.) Every installation I've seen like this uses a couple feet or so of 2" of RNC filled until no more cables will fit. I use a "fill loosely" rule of thumb. I would also run 3 pieces from the panel up to wherever you're going (attic?) to allow for future expansion.
I'd like to hear a real Code junkie's take on this. Maybe there's some wisdom to be found in Mike Holt's forum.
No, each cable shall be secured to the cabinet. Some connectors will allow two cables in each connector...
ONLY IF you meet the following... (which you probably don't... I have yet to see a code compliant installation of this section)
Cables with entirely nonmetallic sheaths shall be permitted to enter the top of a surface-mounted enclosure through one or more non flexible raceway not less than 18 in. or more than 10' in length provided all of the following are met:
(a) Each cable is fastened within 12" of the outer end of the raceway
(b) The raceway extends directly above the enclosure and does not penetrate a structural ceiling.
(c) A fitting is provided on each end of the raceway
(d) The raceway is plugged or sealed
(e) The cable sheath is continuous through the raceway.
(f) The raceway is fastened at its outer end
(g) you meet the allowable cable fill
May be very hard, but very common, and have apparently passed inspection. Can you give me the chapter & verse on that citation? There must be a loophole...