use either a 4 square or a 4 11/16 with a 1/2 plaster ring.
|
|
|
Hey fellas,
Does anyone know of a manufacturer that makes multi-gang (2, 3 or 4 gang)electrical boxes that are 1.5" or less deep? I need them for a basement remodel. 1" furring strips are being used over a concrete wall with 1/2" drywall over that.
I did find some 1-1/4" deep single gang boxes, but they're limited to only single gang.
Thanks,
Jason
use either a 4 square or a 4 11/16 with a 1/2 plaster ring.
If I use a 4 square, I'm unable to mount any devices as they only have screws in the corners and they're 1.5" deep.
Where can I find one that is 1" or 11/16" deep?
Thanks,
Jason
sorry I should have said flat plaster ring and a jumbo plate cover.
You could always use something like this
http://images.acehardwareoutlet.com/...19_07_I_RS.jpg
http://images.acehardwareoutlet.com/...getImage.aspx?
Edited to add
These work well with a plastic cover plate
http://images.acehardwareoutlet.com/...121807I_mk.jpg
Last edited by jwelectric; 01-14-2008 at 11:31 AM.
That first link won't look very nice in a finished basement. The second link doesn't work and the third is 2" thick.
Any other ideas?
I'm afraid I'll have to chip out the concrete behind a 2" device.
Thanks,
Jason
Simply tell them to properly fir it out 1 1/2" and do it with standard shallow boxes.
If it's a basement I don't think you are supposed to chip out block.
The problem your going to have even with 1 1/2 boxes is box fill, the way I see it is a 3x2x1 1/2 box is good for 7.5 cu. in., a 14-2 alone is 6 cu. in, so you wont even be able to install a device and make code... They make a 4" sq. by 1 1/4 which is good for 18 cu in plus the plaster ring... Your going to have to fur the wall out to meet code IMO.
That's kind of harsh, jw. That third one does not, from all the research that I've done, exist in a 1-1/2" depth. So, I challenge you to find me one.
As for the boxes that are made to accept a flat plaster ring that are 1-1/2" deep--that could work. I'll look into that.
Otherwise, I'll just fir out the wall a little more and use a standard box.
Thanks for your help, jw and everyone!
Jason
I personally would have just framed the walls with flat 2x4's, not sure of your building codes and insulation factor, but that could be a whole other issue...
You can get these in 1 1/2 so with a 1/2 in plaster ring you would be fine. if you fur the walls out to 1 1/2 hope this helps you out.
Last edited by Chris75; 01-14-2008 at 03:20 PM.
Hey Chris,
That is a good point, but Carlon makes a box (http://www.*************.com/prod-0010802.html) that is 1-1/4" deep and it's rated at 8" cu in. I've commonly heard that reffered to as a "switch box" and I believe their website says that it meets code for a switch or a receptacle. It has the UL stamp too. Anyhow.
1 14/2+G: 1*2*2+1 = 5
1 Yoke: 1*2 = 2
5 + 2 = 7 < 8.
I believe no clamp is needed for a 1G box. So, is that math ok? I would think that a 2G box that's 1-1/2" would be at least 19.2 cu in. Even 18 shoud be ok though.
2 14/2+G: 2*2*2+1 = 9
2 Yokes: 2*2 = 4
2 clamps = 2
9 + 4 + 2 = 15 < 19.2
What do you think?
Ok, everyone replying all at once! I guess I can't say I'm not getting help.I'm going to try that box, Chris with the flat plaster ring. Thanks.
14-2 w ground would equal 6 cu in, 2 for the black, 2 for the white, 2 for the ground...
device (yoke) would be double volume allowance, based in largest conductor supported by the device. = 4
I would say ney on the cable clamp,
so your up to 10 cu in...
so with a 4" sq new work plastic at 18 cu in, you could have 1 device, and two cables in the box and still be okay.
Last edited by Chris75; 01-14-2008 at 03:36 PM.