Have the meter moved to the gable side. The conduit run that the wires are in would not have to move but just be shortened. Then, install a new 100A panel inside the house on the gable side of the house.
No problem so far, right?
Legally, can the new panel for now have nothing in it but the main breaker, and another say 80A breaker feeding the existing panel? This setup is only temporary, but I'm wondering if that would pass inspection.
Yes. You don't even need the 80 Amp breaker if you use wire adequate for the size of the main in the old panel. The inspector never saw my temporary installation described below because it was gone before it was time to reconnect. Temporary installations are permitted during periods of construction, remodeling, and maintenance. NEC Article 590.
If you play with the service entrance cable, of course the power company has to get involved? How do they cut power to one drop?