    Default # of Honeywell Zone valve

    I currently have 3 zones on my hot water system. These valves run at 24volts from what I have read. I was wondering if I can add 2 more zones to the system? Is there a limit to how many zones the 24 volt transformer can support/power?

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,401

    Default

    Absolutely...the transformer may need to be updated. It should be marked with VA rating, which will indicate how much power it can supply. Each valve will also have a required value. Add up the load, and then compare with what's available. The transformers aren't often particularly expensive or hard to replace, if required. Yours could have enough capacity, but you need to check to be sure. The valve's requirement should be in their spec sheet.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Senior Member rockycmt's Avatar
    Join Date
    Nov 2007
    Location
    New York
    Posts
    129

    Default

    I will do that, Thanks for the info.

  4. #4
    DIY Senior Member rockycmt's Avatar
    Join Date
    Nov 2007
    Location
    New York
    Posts
    129

    Default

    Here are the specs on a new 24 volt transformer.

    http://pexsupply.com/product_dtl.asp...rand=Honeywell
    Voltage: 750 mV
    Connection Type: Spade Terminals
    Lead Length (in.): 35 in.
    Lead Length (mm): 889 mm
    Open Circuit Output (mV): 600 mV to 750 mV
    Resistance: 2.89 ohm
    Temperature Ratings (F): Hot Junction 1400 F
    Temperature Ratings (C): Hot Junction 760 C
    Temperature Ratings (F): Cold Junction 780 F
    Temperature Ratings (C): Cold Junction 416 C
    Includes: push-in clip
    Used With: Q314, Q324, Q327, Q377, Q379, Q382 Pilot Burners
    Tradeline Value: Tradeline
    Ref: Honeywell.com

    What is the actual numbers I need to compare? I do not see a VA reference.

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,401

    Default

    Don't think that is designed for things like zone valves; more like a specific component in the ignition circuit. 750mV spec and the temperature ratings seem to be the telling ones. You need something like this: http://www.pexsupply.com/product_dtl...eywell&cID=282
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    Electrician Chris75's Avatar
    Join Date
    Aug 2007
    Location
    Litchfield, CT
    Posts
    608

    Default

    Quote Originally Posted by rockycmt View Post
    I currently have 3 zones on my hot water system. These valves run at 24volts from what I have read. I was wondering if I can add 2 more zones to the system? Is there a limit to how many zones the 24 volt transformer can support/power?

    If you look at the wattage of the zone valve and the VA of the transformer you can figure out hot many a 40VA transformer will hold, But you can always use as many transformers as needed...

    I really like these Taco Controls, they simplfy the wiring and neaten it up quite nice, take a look... You can get a 6-zone board, which comes with 2 transformers built right in...


    Last edited by Chris75; 12-05-2007 at 01:33 PM.

  7. #7
    DIY Senior Member rockycmt's Avatar
    Join Date
    Nov 2007
    Location
    New York
    Posts
    129

    Default

    Ok, So just to finish this off..

    The total watage of the valves (Simply add them all up) can not exceed the VA of the transformer?

  8. #8
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,401

    Default

    As I understand it, yes. power=volts x amps.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014