    Default No room on busbar

    Hi,

    I'm coming to the end ( I hope) of a rewire on my house. I've got all my new circuits to the panel and have enough room for my breakers but do not have enough slots on the busbar to take all the neutrals and grounds for same. How do I fit a larger one? When I bought the house the neuts and grounds were mixed on the bars, each under it's own screw though is this ok?

    I'm planning to hire an electrician to come check my work but want to have done a bit of researching on this topic first.

    Thanks folks

  2. #2

    Default

    If the neutral is bonded to the box itself, why not just get a ground bar and install all your grounds onto that, thus freeing up all the slots in the present bar for the neutrals?

    Just my 2 worth.

  3. #3
    Senior Robin Hood Guy Ian Gills's Avatar
    Join Date
    Jul 2007
    Location
    USA
    Posts
    2,781

    Default

    You can have two grounds (but not two neutrals) under one screw, possibly more depending on the manufacturers recommendations. This might free up some space.

  4. #4
    DIY Member cruiser's Avatar
    Join Date
    Jul 2007
    Location
    California
    Posts
    44

    Default

    Thanks folks, Ian I'm goning to look at that today thanks for the idea


  5. #5
    Senior Robin Hood Guy Ian Gills's Avatar
    Join Date
    Jul 2007
    Location
    USA
    Posts
    2,781

    Default

    As long as the ground is the same size wire it can be doubled up.

    Sorry, should have clarified that.